Discuss RCD tripping at 1/2 test in the UK Electrical Forum area at ElectriciansForums.net

jeremy

-
Mentor
Arms
Reaction score
222
Testing some new cabinets today which had in them a PDU with a 30mA rcd upfront as main switch. ( We build among other stuff, communications cabinets for highways, railways, etc). First one tested tripped on 1/2 fault current. Tried another cab, same thing. Did a ramp test, (tester is Kewtech kt64), tripped at indicated 18mA, though it felt like it was going at 15mA, but the tester indicated 18 before it stopped. ( I think they test too fast for accurate diagnostics?) I would expect a 30mA RCD to hold until about 21-24, from experience, and would have been disappointed with 18, but for 11 to fail at 1/2? One the one hand, I hope I've missed something ever so simple so that we can ship these cabs tomorrow, but I think I've covered everything. Any thoughts?
 
Did you test at the RCD with no appliances connected? If they are ramping at 18mA then your tester might need calibrating as at 1/2 times it should be outputting 15mA.
 
Just a thought , was the test carried out with all loads disconnected/ isolated ? , could be some leakage in the equipment connected ..
 
might be some leakage on the load, as sintra said, can you test with no load connected?
 
Tested with probes, ( there's something not right about the word "probes"!) at RCD load side, tried another tester, same make, 2 years younger, tried a different test supply circuit, tried swearing at it, a lot, ( that usually works). They're A type , in anticipation of a rectifier being fitted by the client, but that shouldn't affect the test. The way I see it is no matter what the circumstances of the test, whether it's a simulated situation or real, it shouldn't trip at 1/2, it should trip at x1 and x5. Trip times for x1 and x5 were the same if that's any use? Shouldn't be too bothered as I've had enough of running a workshop and am going back into the field ( got a job as a scarecrow!), but strangely I care what leaves the 'shop whilst I'm there.
 

Reply to RCD tripping at 1/2 test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

What should you do if a client has a CU that is a split board protected by 2 * 63Amp 30mA double pole RCCDs, you took Zs and tested both RCCDs by...
Replies
22
Views
2K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Had a real headache of a fault finding job which has left me scratching my head - RCCB on a split load board, supplying 3 circuits (shower...
Replies
20
Views
4K
I had a fault finding job on Thursday, intermittent RCD tripping. 2 actually, there was a 30mA RCD upstream, and a 30mA RCBO protecting the...
Replies
4
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc