I think it would be safer for us to install RCDs that can work for general protection of the fixed wiring installation and consumer so for instance a type A then it should be down to the manufacturer of XYZ product to protect the product with say a type b rcd or Afdd ect. This way you ensure that the consumer will see it every time they use the XYZ product and if it does trip they know where it is to re-set it. Take a washing machine for instance they get used every day, if it was built into the controls it would be easy to find and reset and test. And it would also give the user a secondary protective device in case of fault.
Just an idea can't see manufacturers stumping the bill for that when they can ultimately make it the consumers problem and expense!
 
I agree with @pc1966 about the AFDDs.
AFDDs are great but in terms of making installation safer I'm still failing to see the real benefits. I know they will pick up parrallel arcs but most likely a OCPD or RCD would take care of these, its rare that you get a high resistance joint between L-N that doesn't turn into a dead short.

My issues:
1) At the moment they only go up to 32amps ( no 40amp shower protection which is where they would benifit IMO )

2) only rated for domestic use

3) Need a series arc greater then 2.5amps to operate (Electrium claim 1.5amps I think) so not so good for Led lighting circuits, which they are possibly adding to the new DPC... Even if you had a lighting circuit with a load of 2.5amps the AFDDs would only operate if the arc was near the origin of the circuit.

4) will work on RFCs but only on the connected load to the appliance, still need to remember that a series arc of 2.5amps is needed downstream of the fault so again it depends on where the arc develops.
 
Wylex do a 40A AFDD so that can be covered, but I don't know about others.

Hager have an AFDD add-on to a MCB that could be used in commercial setups, but a major PITA compared to the neat Wylex solution, and some DP ones rasted at 10kA in EU but not for typical CU seen in the UK.

My biggest concerns with them are:
1) Cost. Just now it would add about £1k (or more) to a board change so if it puts off people from doing a CU upgrade that is likely to put more lives at risk than if more CU are upgraded to RCD protection.

2) Testing. there seems to be no standard test for them or MFT that allow you to diagnose problems. AFDD trips, what do you tell the customer? Change it only to find no improvement? Test for faults in the wiring - how? Test for sparking in appliances causing it - how?
 
Wylex do a 40A AFDD so that can be covered, but I don't know about others.

Hager have an AFDD add-on to a MCB that could be used in commercial setups, but a major PITA compared to the neat Wylex solution, and some DP ones rasted at 10kA in EU but not for typical CU seen in the UK.

My biggest concerns with them are:
1) Cost. Just now it would add about £1k (or more) to a board change so if it puts off people from doing a CU upgrade that is likely to put more lives at risk than if more CU are upgraded to RCD protection.

2) Testing. there seems to be no standard test for them or MFT that allow you to diagnose problems. AFDD trips, what do you tell the customer? Change it only to find no improvement? Test for faults in the wiring - how? Test for sparking in appliances causing it - how?
As said before, a standardised testing port should be included. All to rushed forward in my opinion. More equipment to buy in the future, more calibration costs.
 
I agree, I don't think there will ever be an effective way of testing these devices either, We just have to rely on the microprocessor and a flashing LED.

I got it wrong earlier they can be used in Commercial, but the pollution degree is only 2 so consideration is needed.
 

Reply to RCD Types, Ticking time bomb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
965
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
845
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
2K
My builder has sprung a job on me. New circuit required for a hob. The CU has a single 30mA RCD, type AC. I am still unsure exactly when I should...
Replies
4
Views
1K
Hi, I'm back in the electrical game after 9 years break so feeling a little rusty! I'm adding an additional socket to a circuit but the main RCD...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock