Ever since I went to my sisters place and did some tests and found her 30 ma rcd welded shut I have always had doubts
about relying solely on 1 rcd, especially in a garden, at least with my sister she had a low enough EFLI to trip an mcb in the event of an earth fault, in a garden
that is TT'd you would not have that luxury, the circuit would simply not switch off in the event of an earth fault and would remain live until someone touched something metal.

This garden already has an existing underground cable but somewhere along the line someone has buried an underground joint to extend this cable and the readings I get from testing are very erratic.

The Line to neutral IR resistance jumps from being at 0.2 M Ohms up to about 2.5 M Ohms at 500 V and sort of flitters about between these two extremes and won't settle.
The existing underground cable is a two core roughly 6mm but in reality is an older multistrand cable with the armour used as the cpc.
The armour has broken down and I get an end to end resistance reading of 12 Ohms on the armour, the cable is only 15 metres long so it really does look like this underground joint has got water contamination and the cable should be abandoned IMHO.

There are three small buildings in the garden, one greenhouse, one shed and a sort of chalet, he wants power to all three.

The greenhouse will be damp with a floor that is basically real earth IE the garden soil.
The shed will also be damp but has a wooden floor leading out onto decking.
The chalet seems quite dry with a wooden floor also.

I'm thinking the best way to do this would be to run a new cable which is going to be really hard but I never thought of using trunking to conceal this cable from the fuse board to the outside of the house. This is a good idea as long as I can get some nice skirting trunking maybe, I will have a look today so thanks for the suggestion.
Once the cable is outside the house I can then surface clip or bury it around the perimeter of the garden down to the end.

At the moment I think the best method would be to run a new supply in trunking (not easy) protected by a 100 ma S type.
This would go to a central distribution point in the garden somewhere.
From there I could run a supply to the greenhouse and rod it there.
From the central point I could also run a supply to the shed and rod there also.
Also run a supply to the chalet and again rod it.
This would give me three rods in the garden at different places which should give me a better overall Ra reading.
The main house supply cable is under ground TN-S with a lead sheath that is terminated at the MET in the house so this should also help lower my Ra readings (the lead sheath of the supply cable runs underground through the garden)
Each garden building would have its own small CU and each small CU would be protected by a 30 ma RCD.

The other way I was thinking would be to bond everything and export the main bonding from the house but I would have to put a ground mat down in the greenhouse
to bond the floor to the frame but if I managed to extend the bonding from the house at least I could use the low EFLI of the supply circuit IE not TT anything so that if an rcd did fail in the event of an earth fault I would have the added protection of an MCB tripping at the main fuse board in the house.
Bonding everything in this damp garden enviroment seems a bit hit and miss to me especially with the damp and possibly kids running around in bare feet so this idea gives me the willies a bit, I mean how can I make the whole garden an extension of the house equipotential zone especially when he wants a couple of outside sockets installed?

I am going to do a bit more testing today.

As far as part P goes I would like to wait until after my assessment but if the guy really wants me to get a shift on I will have to notify LABC before I start and pay the fees.

Any thoughts on this one?

Thanks for taking the time to read this lengthy post.

Hi La Poste, great post, great to read someones thought processes, very interesting problem. Chewy I'd say. And they're the best aren't they! (chewy ones)

Can you not preserve the TNS earthing system (you know the one, the one that was used until the 70's when all of sudden the laws of physics changed and it WAS after all, safe to use your Neutral as an earth!) and simply use that, run a length of 4 10-or-more mm2 core armoured? Then you're best practise not relying on the armour for your earth (but will be using it as well anyway), you have a separate core should you wish to run an extra bond back to the MET in the house, and ...no type S RCD up front needed. Assuming a good Ze of course.


Just an idea. And if armoured probably no need to trunk (except aesthetics), as long as you use cleats and not tape :drool5:
 

Reply to RCD's in series in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
535
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock