Discuss RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

S

Sparkz123

Hi,

I have a problem with 17t edition consumer unit (MK Sentry) on a TT system that has completely left me baffled. I'd be very grateful for an advice.

On the left hand side of the board I have a 100 amp main switch. Immediately next to that a 30ma RCD controlling 3 MCB's and 2 spare ways, followed by a second MCB controlling 4 MCB's and one spare.

If I test the3 left hand circuits the L/H RCD fails to operate, it also fails to operate when tested from the board. If I test any of the circuits controlled by the R/H RCD both RCD's trip. If I swap the RCDs around nothing changes, the L/H one fails to operate unless the R/H one is tested.

All my neutrals are connected to the correct connector blocks and there are no IR readings between the two blocks.

To leave the entire installation RCD protected overnight I swapped the main switch and L/H RCD's around, so the main switch was an RCD, but this failed to operate, even though it was fine when controlling the L/H circuits.

I'd appreciate any input.

Thanks,

Pete.
 
Disconnect all circuits from the board and carry out RCD tests with prods , see what happens , if all works correctly for both RCDs then its an issue with your wiring , or faulty RCDs ,
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.
 
It may or may not be relevant here, but I recently installed an MK Sentry dual RCD board, where one RCD failed to trip on test. I had to leave the installation covered by the one good one as it was getting dark.

probably decided to trip at last and take the lights out.
 
Any chance of a picture of the CU close up I take it you have checked and double checked that its connected up correctly !!!!

Just out of interest what is your RA at the board ?
 

Reply to RCD's Misbehaving in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
378
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
366
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
558
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
271
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock