Hi all - hopefully you can forgive my lack of knowledge on electrics, I have a basic grasp but am no expert.

The issue I've had and am looking for an initial steer on is that during some extremely heavy rains recently, after a long spell the RCDs will trip. While still raining, they will not be able to be reset, but a little after it stops, they can be, and work fine.

As a bit more info, this is in a top floor apartment, and there is a very small amount of visible water penetration during heavy rains over the main door from the stairs, which is in the vicinity of the Consumer Unit, and likely where the main incomer passes.

I've read through the other posts on RCDs tripping here, and it sounds like there could be a number of things. Given that it's the RCDs that are tripping (and not always at the same time), I think the issue has to be downstream of the CU. But thereafter, I'm guessing that the fault could be anywhere. All appliances work fine under normal conditions, no tripping. So I'm thinking that there is some faulty cabling going through an area that during rains is getting wet enough at some point to cause some current leakage to something, and trip the RCD. And then once the moisture dissipates, the leakage goes, and can be reset without issue. And if this is the case, then it's very difficult to pinpoint, therefore meaning I could be in for a full rewire?

At the minute the CU has two banks of circuits, each covered by an RCD, so I'm wondering if in lieu of full rewire it would be easier to change the CU and layout so each circuit has it's own RCD, which would then at least focus the issue, and stop me losing full electrics hopefully when this issue arises, until such time as I can resolve the externals to stop water penetration 100%. I'm concerned about the full rewire as there are a lot of original walls which the cabling will be chased into, which is obviously messy work and it'll tear the place apart to have to do so.

Any ideas on how you would start with this type of issue? Many thanks in advance!
 
Hi all - hopefully you can forgive my lack of knowledge on electrics, I have a basic grasp but am no expert.

The issue I've had and am looking for an initial steer on is that during some extremely heavy rains recently, after a long spell the RCDs will trip. While still raining, they will not be able to be reset, but a little after it stops, they can be, and work fine.

As a bit more info, this is in a top floor apartment, and there is a very small amount of visible water penetration during heavy rains over the main door from the stairs, which is in the vicinity of the Consumer Unit, and likely where the main incomer passes.

I've read through the other posts on RCDs tripping here, and it sounds like there could be a number of things. Given that it's the RCDs that are tripping (and not always at the same time), I think the issue has to be downstream of the CU. But thereafter, I'm guessing that the fault could be anywhere. All appliances work fine under normal conditions, no tripping. So I'm thinking that there is some faulty cabling going through an area that during rains is getting wet enough at some point to cause some current leakage to something, and trip the RCD. And then once the moisture dissipates, the leakage goes, and can be reset without issue. And if this is the case, then it's very difficult to pinpoint, therefore meaning I could be in for a full rewire?

At the minute the CU has two banks of circuits, each covered by an RCD, so I'm wondering if in lieu of full rewire it would be easier to change the CU and layout so each circuit has it's own RCD, which would then at least focus the issue, and stop me losing full electrics hopefully when this issue arises, until such time as I can resolve the externals to stop water penetration 100%. I'm concerned about the full rewire as there are a lot of original walls which the cabling will be chased into, which is obviously messy work and it'll tear the place apart to have to do so.

Any ideas on how you would start with this type of issue? Many thanks in advance!
Sounds like you have water ingress into your flat, getting stuff damp and causing the RCD to detect a fault due to damp in your flat, need to call an electrician to survey the problem.
 
You need to employ a builder to investigate where the rain's coming in.
IP20 electrics and water don't go together.
a builder???? bugger that. end up with more problems than he started with. get a sparks in first. find out where the problem is, then get bob the builder to fix the leak.
 
Sounds like you have water ingress into your flat, getting stuff damp and causing the RCD to detect a fault due to damp in your flat, need to call an electrician to survey the problem.
Thanks all for the quick responses! Yes, 100% the issue is caused by water ingress. I'm just wondering how an electrician would approach this. And I have the issue that it only occurs after a sustained downpour, so getting a electrician out at the time of it tripping is a near impossible thing to try and time. For example, yesterday when this occurred was late at night during a heavy storm (weather warnings and all the rest) - not something that is predictable. If I can get someone out when it's tripped, then surely you can't work as there is water ingress around the CU and it's not safe, and at any other time the fault is gone, so impossible to diagnose.

I completely understand that this is in need of a good, qualified spark, but I'm just conscious that if I call them now, when it's dry and the issue is not present (which is 99.9% of the time), they wouldn't have much to go on. Which could mean that we'd end up just looking and saying, 'yes, there must be an issue, but no way of finding out where'.

Investigate first knock out wall after.
Out of interest, how would an electrician go about diagnosing this? Take apart the CU and inspect? Like I say, under normal conditions there are no issues and all works fine. Are there other ways to test circuits for faults that would trip an RCD that can be done non intrusively?

Thanks again.
 
Hi all - hopefully you can forgive my lack of knowledge on electrics, I have a basic grasp but am no expert.

The issue I've had and am looking for an initial steer on is that during some extremely heavy rains recently, after a long spell the RCDs will trip. While still raining, they will not be able to be reset, but a little after it stops, they can be, and work fine.

As a bit more info, this is in a top floor apartment, and there is a very small amount of visible water penetration during heavy rains over the main door from the stairs, which is in the vicinity of the Consumer Unit, and likely where the main incomer passes.

I've read through the other posts on RCDs tripping here, and it sounds like there could be a number of things. Given that it's the RCDs that are tripping (and not always at the same time), I think the issue has to be downstream of the CU. But thereafter, I'm guessing that the fault could be anywhere. All appliances work fine under normal conditions, no tripping. So I'm thinking that there is some faulty cabling going through an area that during rains is getting wet enough at some point to cause some current leakage to something, and trip the RCD. And then once the moisture dissipates, the leakage goes, and can be reset without issue. And if this is the case, then it's very difficult to pinpoint, therefore meaning I could be in for a full rewire?
I agree with the previous posters that it's almost certainly going to require a professional to help you here. You did well to begin the faultfinding process by noting the pattern of the intermittent fault which is clearly related to heavy rain. 90% of these faults are related to outside lights, usually garden lightds but obviously a top floor apartment won't have too many of those. Any wall lights on your rcd?. If you have none of the above than time to call in a spark and having him around while the fault is still IN the system will save you and him headaches
 
Any water ingress around or in the consumer unit will leave clues . A good electrician will find it. You should not have to wait till it is tripping.
 
Any water ingress around or in the consumer unit will leave clues . A good electrician will find it. You should not have to wait till it is tripping.
Not always true.
if it’s intermittent it can be a bit of a b*gger to find sometimes.
testing can Sometimes show nothing out of normal when it’s not raining. just one drip of water or ingress to a certain point may be the cause.
 
Thanks all for the quick responses! Yes, 100% the issue is caused by water ingress. I'm just wondering how an electrician would approach this. And I have the issue that it only occurs after a sustained downpour, so getting a electrician out at the time of it tripping is a near impossible thing to try and time. For example, yesterday when this occurred was late at night during a heavy storm (weather warnings and all the rest) - not something that is predictable. If I can get someone out when it's tripped, then surely you can't work as there is water ingress around the CU and it's not safe, and at any other time the fault is gone, so impossible to diagnose.

I completely understand that this is in need of a good, qualified spark, but I'm just conscious that if I call them now, when it's dry and the issue is not present (which is 99.9% of the time), they wouldn't have much to go on. Which could mean that we'd end up just looking and saying, 'yes, there must be an issue, but no way of finding out where'.


Out of interest, how would an electrician go about diagnosing this? Take apart the CU and inspect? Like I say, under normal conditions there are no issues and all works fine. Are there other ways to test circuits for faults that would trip an RCD that can be done non intrusively?

Thanks again.
There may be visual clues like water staining or corrosion at the affected area.

Finding the affected area when not tripping is where the problems begin.

I've done many of these and sometimes you get lucky and find a leaky outside light or a rusty backbox and socket.

There are tests that can be done that may give an indication but only may.


My favourite,

A dentists that found their sockets would trip on Fridays occasionally. Would call the fault in and by the time an electrician attended it reset, every time.

I got approval to go in on a Saturday and do a lot of testing and found that the Insulation Resistance of all the cables was very good with the exception of one section of the socket ring.

It still worked but was significantly lower than everything else.

The cleaner popped into the room to change the air fresheners (???) and commented that it "didn't smell too bad in here today"

Whats this about a smell I asked, "Oh it usually stinks in here"

Found a section of floor, under a cupboard, I could lift and....

...yes, under the floor was full of sewerage..gip gip puke.

It was slowly filling up over the week, probably submerge a junction box and trip, and would seep away over the weekend.

Wasn't going to mess around so just disconnected the section and rewired it on the surface in trunking.

Apparently the turd herders had to pump 20,000 litres of sewerage and scrape a couple of tons of solids out from under the floor before finding a completely sheared soil pipe.

I always think of those poor sods when wallowing in a pit of self pity about having to work in the rain or somesuch.
 
@Paignton pete
I take your point , but he says -As a bit more info, this is in a top floor apartment, and there is a very small amount of visible water penetration during heavy rains over the main door from the stairs, which is in the vicinity of the Consumer Unit, and likely where the main incomer passes.
He also indicates that both RCD's are tripping.
 
The water could even be inside the consumer from the way you describe the issue.
First port of call is to have an electrician in to assess the situation.

Any water ingress around or in the consumer unit will leave clues . A good electrician will find it. You should not have to wait till it is tripping.
That is true. A quick visual will establish. In practice it is rare for the issue to be at the CU as the physical distance between the conductors( Lives and earths) tends to not lend itself easily to these types of faults. Often however the distance between socket neutral and earth bar is close and worth investigating. Neutral earth faults don't tend leave conspicuous marks like a live earth fault would so a keener eye is required
 
There may be visual clues like water staining or corrosion at the affected area.

Finding the affected area when not tripping is where the problems begin.

I've done many of these and sometimes you get lucky and find a leaky outside light or a rusty backbox and socket.

There are tests that can be done that may give an indication but only may.


My favourite,

A dentists that found their sockets would trip on Fridays occasionally. Would call the fault in and by the time an electrician attended it reset, every time.

I got approval to go in on a Saturday and do a lot of testing and found that the Insulation Resistance of all the cables was very good with the exception of one section of the socket ring.

It still worked but was significantly lower than everything else.

The cleaner popped into the room to change the air fresheners (???) and commented that it "didn't smell too bad in here today"

Whats this about a smell I asked, "Oh it usually stinks in here"

Found a section of floor, under a cupboard, I could lift and....

...yes, under the floor was full of sewerage..gip gip puke.

It was slowly filling up over the week, probably submerge a junction box and trip, and would seep away over the weekend.

Wasn't going to mess around so just disconnected the section and rewired it on the surface in trunking.

Apparently the turd herders had to pump 20,000 litres of sewerage and scrape a couple of tons of solids out from under the floor before finding a completely sheared soil pipe.

I always think of those poor sods when wallowing in a pit of self pity about having to work in the rain or somesuch.
This example highlights the value of good electrical "detective work". There is no electrical meter or classroom teaching that can solve this type of problem otherwise.
 
.


My favourite,



Apparently the turd herders had to pump 20,000 litres of sewerage and scrape a couple of tons of solids out from under the floor before finding a completely sheared soil pipe.

I always think of those poor sods when wallowing in a pit of self pity about having to work in the rain or somesuch.
Classic . ;)
 
It would be nice to know exactly what's causing the tripping, and whether a bodge can be done to stop it happening, but the basic problem here is electrical equipment of insufficient IP rating for the environment that it's operating in. IP20 equipment in a place that requires a minimum of probably IP43.
The solution is to change the environment, not the equipment, then the problem will go away.
It would be different if MCBs were tripping. That would be causing permanent damage, in the form of carbonisation somewhere.
 
Hi guys - thanks to everyone for their input, really helpful! Like I say, I'm fully aware that I need a good electrician to look at it, but I just wanted to understand a bit more first and make sure that there would be something to look at under 'normal' conditions. Which by the responses sounds like there should be something to go on hopefully.

For anyone that's interested, attached are a few images. The wall on which the CU is mounted is internal (bedroom behind), and roof terrace is directly above. Main water ingress can be seen at the top, and these are solid masonry walls (old random rubble, circa 100 years old), but will be little stopping it moving through slowly through once it's in. Like I mentioned, the CU has 2 banks each covered by an RCD, which don't trip at the same time. It was asked about the exterior lights / sockets for the roof, and actually these are on the side which is less prone to tripping funnily enough. The side that trips first is that with the sockets, and water heater (which now thinking about it is located upstairs in an enclosed cupboard...that could be a good place to start!).

Thanks again for all the responses, really appreciated!

IMG_4121.jpg
IMG_4122.jpg
 

Reply to RCDs tripping during heavy rains in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
742
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
877
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock