Knowing it was going to be covered with insulation, was any containment considered? Oval, conduit will both greatly improve heat dissipation and should have been factored in with the cable calc design. Who designed the install?
 
Didn't give you a reference method whilst on the phone, did they? What's your answer from the BS7671 for the method? Table 4A2 has all the stipulations for deciding and the U value of your insulation.
 
Sounds and looks like 103 to me too. Vastly reduces the ccc. Were the sizes correctly selected for the install in your mind?
 
Job done, happy with the install. Anything special about it to show off photos?
 
Knowing it was going to be covered with insulation, was any containment considered? Oval, conduit will both greatly improve heat dissipation and should have been factored in with the cable calc design. Who designed the install?
Polite question honestly, are your comments regarding installing the cables in oval conduit and then enclosing them in insulation, the same as you would use for cables in an insulated roof space, or an insulated wall in a normal domestic traditionally built house? because in my humble opinion installing cables in insulation, is a problem but enclosing them in conduit, would this not compound the problem. I have no experience of timber framed houses by the way, maybe I'm missing something?
 
Any movement of air in a problematic space, to increase the dissipation of heat from a cable that is carrying a current in a timber framed house, in my opinion, will improve the longevity and the performance of the cable. 50x50 trunking down a 2.5 metre wall would only help that heat release, again, in my opinion - I'm still learning!
 
Any movement of air in a problematic space, to increase the dissipation of heat from a cable that is carrying a current in a timber framed house, in my opinion, will improve the longevity and the performance of the cable. 50x50 trunking down a 2.5 metre wall would only help that heat release, again, in my opinion - I'm still learning!
For an example a 2.5mm twin and earth cable in a wall in insulation will take 13.5 amps were as twin and earth in conduit in insulation it will take 20 amps so yes you are correct :)
 
Also I think that if you are involved with the planning stage of the install then this is something that could be implemented and the cost of the containment would be taken up by the savings in CSA of the cable. I may have to remove my rose tinted specs but it seems good practice and safe practice.
 
Oval, conduit will both greatly improve heat dissipation and should have been factored in with the cable calc design.

Any movement of air in a problematic space, to increase the dissipation of heat from a cable that is carrying a current in a timber framed house, in my opinion, will improve the longevity and the performance of the cable. 50x50 trunking down a 2.5 metre wall would only help that heat release, again, in my opinion - I'm still learning!

Sure, if you have to run a cable vertically through insulation, then putting it in 50x50 trunking may well allow it to run cooler, but only if the top, and preferably the bottom, are open to the air. Stuffing a piece of T&E in a bit of oval tube isn't likely to make much difference given the limited space available for convection, and may make it worse.
 
For an example a 2.5mm twin and earth cable in a wall in insulation will take 13.5 amps were as twin and earth in conduit in insulation it will take 20 amps so yes you are correct :)

I think the difference here is whether the cable or conduit is touching the (relatively thermally conductive) inner wall or not. Table 4D5 shows that the same cable in insulation but touching the inner wall is rated at 21A.

See also 4A2 for diagrams showing the various possible configurations.
 
I would say the best design is use method 102 , touching the inner wall surface, that way it looks like the standard cable sizing will still be within tolerance for you standard circuits in a house, but if the op has used method 103 he may have to rate ring circuits to 20amps if he has used 2.5mm twin and earth
 
Polite question honestly, are your comments regarding installing the cables in oval conduit and then enclosing them in insulation, the same as you would use for cables in an insulated roof space, or an insulated wall in a normal domestic traditionally built house? because in my humble opinion installing cables in insulation, is a problem but enclosing them in conduit, would this not compound the problem. I have no experience of timber framed houses by the way, maybe I'm missing something?
I agree Pete I was a bit lost on that, if you enclose a cable in any type of conduit the ccc is further reduced. It ain't going to act as a heat sink is it.
 
I agree Pete I was a bit lost on that, if you enclose a cable in any type of conduit the ccc is further reduced. It ain't going to act as a heat sink is it.
Well I was a bit skeptical to be honest, Westward 10
 
Well I was a bit skeptical to be honest, Westward 10
I think people worry too much the chance of lighting circuits and ring finals overloading to such a degree in a domestic property because of thermal insulation must be pretty small. I would probably consider shower circuits and the like more of a problem.
 
We are not talking of a particular circuit type here and I agree that lighting and power circuits would not be an issue due to true usage but taking your shower that has a cable route through a full height wall and a little bit more, if 10mm
64amp clipped direct
32amp just stuffed in't middle of it all
44amp in some sort of conduit in't middle of all the insulation.
That's the difference between a nice powerful warm 9.5kw for me and a piddly 7.5 kw for you. There is something in it for fixed loads.
 
We are not talking of a particular circuit type here and I agree that lighting and power circuits would not be an issue due to true usage but taking your shower that has a cable route through a full height wall and a little bit more, if 10mm
64amp clipped direct
32amp just stuffed in't middle of it all
44amp in some sort of conduit in't middle of all the insulation.
That's the difference between a nice powerful warm 9.5kw for me and a piddly 7.5 kw for you. There is something in it for fixed loads.
Am I missing something, how does the ccc increase by 12A because the cable is contained in conduit.
 
Look in the tables - it gets reduced from 64 to 44 if contained and in insulation but reduced from 64 to 32 if placed just in insulation. Come on westward did you have a heavy lunch?
 
Putting on my tin hat, I reckon the good book says no advantage for using conduit in insulation, advantage comes from clipping cable or conduit to the wall. Little pic to illustrate :

IMG_0361.JPG
 
Okay you are looking at Table 4D5. Your 44A comes from column 7, enclosed in conduit in an INSULATED WALL. Your 32A comes from column 5, in a stud wall with THERMAL INSULATION. Column 7 does not refer to thermal insulation it refers to an insulated wall. None of the Installation Methods in that table refer to cables in conduit surrounded by thermal insulation. Your sums are incorrect.
 
Putting on my tin hat, I reckon the good book says no advantage for using conduit in insulation, advantage comes from clipping cable or conduit to the wall. Little pic to illustrate :

View attachment 33743
Was just looking at the same thing, but it refers to a thermally insulated wall much like column 7 Table 4D5. So from your shown Table you would refer to column 2 in 4D2A which give an amp or so is the same as 4D5.
 
Okay you are looking at Table 4D5. Your 44A comes from column 7, enclosed in conduit in an INSULATED WALL. Your 32A comes from column 5, in a stud wall with THERMAL INSULATION. Column 7 does not refer to thermal insulation it refers to an insulated wall. None of the Installation Methods in that table refer to cables in conduit surrounded by thermal insulation. Your sums are incorrect.

Yes it does. Column 7 reference method A* for full installation method refer to table 4A2 number 2 but for flat twin and earth cable.

4A2 number 2 multicore cable in conduit in a thermally insulated wall with an inner skin having a thermal conductance of not less than 10 W/m2K c. So you use reference method A to determine CCC.
 
Last edited:
Yes it does. Column 7 reference method A* for full installation method refer to table 4A2 number 2 but for flat twin and earth cable.

4A2 number 2 multicore cable in conduit in a thermally insulated wall with an inner skin having a thermal conductance of not less than 10 W/m2K c. So you use reference method A to determine CCC.
I can see your point but it does not refer to thermal insulation but a thermally insulated wall. Not going to cross swords here my initial confusion was from an earlier post which stated containing the cable in conduit would increase the ccc, and I assume the poster was misguided by Table 4D5.
 
To add my measly morsel, 7.1 Reference method A, is described as 'wall consists of outer weatherproof skin' etc etc, which suggests to me is for an external wall. Whereas Reference method 102 - 103 are referring to stud walls, and placing in conduit will have no beneficial or detrimental effect to ccc, apart from bunching of cables?

OR should I just carry on cooking me piece of beef :rolleyes:
 
Beef in. Most of the wood stud work installations I've seen or done have the cables down the middle of said stud work and would never be close to the inner wall surface.
 
Beef in. Most of the wood stud work installations I've seen or done have the cables down the middle of said stud work and would never be close to the inner wall surface.
No Mate run it in some trunking or conduit that will increase the ccp of the cable.
 
Spuds in. You've confused me now Pete, thought the whole thrust of this debate, suggest no benefit of putting cables in conduit in insulated stud wall?
Trying to be sarcastic, but obviously it didn't work
 
For those interested in my culinary adventure, cauliflower cheese in, braised cabbage in, blackberry up side down cake (her in-doors is doing that), arrrgggh hate Sundays. Wot was the question again?
 
For those interested in my culinary adventure, cauliflower cheese in, braised cabbage in, blackberry up side down cake (her in-doors is doing that), arrrgggh hate Sundays. Wot was the question again?
I am actually in the garden in the October sun, glass of wine with roast lamb on the go.
 
Ive had it thanks I'm gone the insulation is getting to me, as well as the heat, I#m going to thread myself in some oval conduit to make me cooler.
 

Reply to Reference Meathod for Timber Frame in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All I wanted to ask a question about the reference method. Passing wiring through holes made at 0.2-0.4 of the joist span. The cables passes...
Replies
1
Views
1K
Hi guys After some suggestions. My next job will be to wire a new timber frame extension throughout. My questions are any tips for running...
Replies
6
Views
1K
Quite a few new builds are popping up locally in my area. I have noticed that they are not even being first fixed until the buildings are...
Replies
1
Views
873
Hi, just wondering if I have a cable passing through "100mm insulation at 2 points", do I use the correction factor of 100mm at 0.78 or 200 at 0.63
Replies
0
Views
327
Hi All I would appreciate some help with a few questions here regarding cables sizing, I'm using the latest 18th edition, amendment 2. Q1...
Replies
0
Views
931

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock