I'd disconnect the 13A sockets each side of the CU and then measure R2 end to end from each socket. One test round the ring. The other test to and from the CU. With the CU CPCs for the RFC still disconnected at the CU.
That should give a sensible remainder of ring R2 and isolate the issue in the cables going to and from the CU.
You may need a wander lead of course.
 
I'd disconnect the 13A sockets each side of the CU and then measure R2 end to end from each socket. One test round the ring. The other test to and from the CU. With the CU CPCs for the RFC still disconnected at the CU.
That should give a sensible remainder of ring R2 and isolate the issue in the cables going to and from the CU.
You may need a wander lead of course.

Ehhh? Soulsurfer has found the 'fault' :)
 
Carrying out tests on new builds we have been carrying out, get first test cert over from sparks on site LL & NN look good earth way down low, then remembered metal walls caddy straps light circuits ect.
Few days later same site different sparks phone call same as above been checking everything he tells me I mention parallel paths & phone goes silent the penny drops oh S...t of course.
Not quite as low as fist post but quite low.
See it on the test sheet kitchen all good block walls, tin in the up & downstairs rest of house so 2 rings affected.
 
Extended most of the circuits from old 3036 board to new board and used a box with din top hat mounted creating a huge earth bus bar in effect :rolleyes: felt a right prat

SS, I read this post all the way through thinking what could it be, and you led us on a right merry dance mate! Prat is correct! But we all can't see the woods for the trees every now and then! My initial thought was both legs going through one back box near the CU, with the CPCs joined there, as I have seen that sort of thing before. Well done for, ahem, finding it! ;)
 
Extended most of the circuits from old 3036 board to new board and used a box with din top hat mounted creating a huge earth bus bar in effect :rolleyes: felt a right prat
Maybe you could add this to the never have i ever thred , we have all done some silly things in the past , at least what you have done is not dangerous and you found what was coursing your low reading before you stripped the installation down back to its component parts . :)
 
Maybe you could add this to the never have i ever thred , we have all done some silly things in the past , at least what you have done is not dangerous and you found what was coursing your low reading before you stripped the installation down back to its component parts . :)
Was just getting to that Flanders was taking all the sockets off ! Oh dear, any better ways to extend cables to new boards without din rail would be a go ! Ha ha, just wanted a secure connection rather than box of wagos or crimps! As customer didn't want to go full rewire, would've been far easier and more cost effective.
 

Reply to Renovated house low r2 readings ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
733
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock