Discuss Replacing 12v MR16 (not IP rated) with GU10 IP65 rated downlights in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
Hi, I have to replace bath and shower downlights to IP rated. I thought they were GU10 so bought the GU10 fitment and bulbs. I fitted it and it did not work ? I then found out the original fitment is MR16 12v. Please can someone tell me if I need to buy IP rated MR16 downlights and LED MR16 bulbs OR can I continue with the GU10s - please let me know what best to do. Thanks
 
If all parts of the lamps are 2.25m or more from the floor, then, although it is preferable that they are IP rated, they are not required to be.
To answer your original question, it depends on whether the original lights were wired with remote 12 volt transformers, serving more than one light, or whether they were wired with individual transformers for each light. Remove a fitting from the ceiling, pull very gently on the wire attached to it, and see if a transformer falls out of the hole. If so, the old light and transformer can be discarded, and the cable that was attached to the transformer can feed the new lamp, if it's long enough, following the manufacturer's instructions.
 
If all parts of the lamps are 2.25m or more from the floor, then, although it is preferable that they are IP rated, they are not required to be.
To answer your original question, it depends on whether the original lights were wired with remote 12 volt transformers, serving more than one light, or whether they were wired with individual transformers for each light. Remove a fitting from the ceiling, pull very gently on the wire attached to it, and see if a transformer falls out of the hole. If so, the old light and transformer can be discarded, and the cable that was attached to the transformer can feed the new lamp, if it's long enough, following the manufacturer's instructions.
Thanks a lot for this. We will go and have a look tomo and hopefully it will just be a transformer at each light and we'll be ok. The EICR failed on these alone so wew have to get them done but I will check that height. Thank you.
 
Failed on : 8.6 Suitability of equipment for external influences for installed location in terms of IP rating: C2

(4.4 Consumer unit made from combustible materials​
) (C3 )​
(Consumer unit )​
(4.17Absence of RCD in 7 final circuits​
) (C3 )​
(Consumer unit )​
(8.1 a)Absence of RCD in lighting circuit​
) (C3 )​
(Consumer unit )​
(8.6 Light not suitable for location​
) (C2 )​
(Bathroom )​
(4.17Absence of RCD in 7 final circuits​
) (C3 )​
(Consumer unit )​
Immediate action required for items: ( N/A Urgent remedial action required for items: ( 4​
 

Reply to Replacing 12v MR16 (not IP rated) with GU10 IP65 rated downlights in the Lighting Forum area at ElectriciansForums.net

Similar Threads

  • Article
Electrical2Go - Mega Downlight Deal - Don't miss out! Taking place from August 18th to 20th, we're offering an incredible promotion for...
Replies
1
Views
623
Hi there, I'm a competent DIYer that has done lots of with lighting over the years but have just moved into a house packed full of mr16 halogens...
Replies
15
Views
9K
Hi all, Im new to the forum and wanted to check something and maybe get some advice confirmation. Ive got halogen wall lights which use a...
Replies
6
Views
1K
Just popped round to a neighbours house, they have several of these in the kitchen that have failed...
Replies
5
Views
1K
I have 60+ of these Aurora down lights in 12v MR16 format and want to convert them to 230V GU10 LED by changing the lamp holder for something like...
Replies
9
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock