Discuss Replacing run to detached garage sub panel. in the UK Electrical Forum area at ElectriciansForums.net

mikeshums

DIY
Reaction score
4
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit (about 15 ft) and can see it fried on the detached garage side. I suspect age, critters and or water got to it and shorted it out.

If I replace the wire from the sub-panel back across the walkway what is the requirement for creating a junction at the point it leaves from the main house? I'm hoping that it's not required to do a single intact new run all the way back to the main service box in the house. thanks.
 
You could use a weather proof rotary isolator.
 
I would suggest an insulation test on the cable you wish to re-use back to the main board to verify its still in good condition, this will probably need the use of a MFT which all electricians will have.
 
So this was resolved. I used a line tester to see if I had power across the breaker on the main box in the house. Breaker tested fine. Then I checked power along the line and found that I had power exiting the house but no power entering the detached garage. I pulled the cover off the conduit box and saw it was burnt through. Mice (2 carcasses :) ) Junction box on the house side, new wire to the sub-panel and we're in business.
 

Reply to Replacing run to detached garage sub panel. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
732
I am adding a 60 AMP subpanel for a detached garage/workshop with a 200 foot underground conduit run from the main panel to the sub panel...
Replies
3
Views
895
I’m planning to run an electrical sub-panel to my detached garage (about 150’ away) and run it off my 200 amp home panel. I live out in the...
Replies
8
Views
1K
I recently purchased a rural property in Arizona. The property receives power from APS, the local electric utility. Power arrives from the...
Replies
3
Views
862
I want to verify if the breaker size is correct for the service going into my detached garage. I have 6 AWG cable going from my main panel in my...
Replies
0
Views
979

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock