Good morning all. So question; if you’re making additions to an existing circuit, but the new cable is not min 50mm deep in wall or mechanically protected and the current circuit is not RCD protected do you tell customer that RCD protection is required as per the regs? My thought is yes and explain why it’s needed to customer; if they don’t want it then I’d walk away but just want to hear others views. TIA
 
So adding 3 new double sockets in to existing ring but one of the sockets in the wall cannot go 50mm deep. Oval conduit isn’t really mechanical protection.
 
Yep, there the option for that possibly. My post was really to answer a question I had with another spark about some work being done. My view was it needs either proper mechanical protection (metal conduit) or (a future proof measure) RCD protection.
 
For me, with the new regs I always where applicable advise customers about the need for RCD protection. Some jobs I win, some I lose as there’s always someone willing to just wire it up and then throw smoke.
 

Reply to Requirements for RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
845
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
584
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
971
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock