Discuss Rewiring 40-50 year old wiring in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Hi all,

As the title, just after a couple of pointers. Basically I've just bought a house, the existing wiring is the old colours but the CPC has a dark green sleeve, on top of that there is only 3 circuits for the house, a power a lighting and a 16a radial feed to the kitchen?
I've had a face plates of the socket and there is only 1 no. Socket in both bedrooms, and the middle floor is on a ring, whereas the top floor socket has been spurred off it, the plan was just to add some sockets but without spurring of a spur it looks like the ring will have to be reconnected. So I'm tempted to get a rewire, as it's going to start getting to that price with adding new sockets and the wiring bring 50 years old.

My main question is the consumer init, at the moment Ive got a plastic boxed (should be metal) unit with only one RCD and appropriate bonding to the 17th, I know ideally you'd have two RCD but to save 500 odd quid I'm wondering if it's compliant leaving alone because its existing.

Really appreciate any advice given.

Thanks
 
if you are going for a rewire, then :
1. you can have more sockets where you need them
2. lighting can be upgraded to your needs. e.g. downlights
3. an upgrade of the CU will be less than £500 as part of a rewire, unless you go for RCBOs for each circuit, which, in the scale of things, is advisable. for a 3 bed semi, the total cost should be around £4k -£5k depending on the extent of the works.
 
Just a thought - if you don't have the funds to pay outright for a full wire then obtain three estimates and with them go to see you bank manager for a loan to pay for the work. That's what my friend did and had no trouble obtaining a loan. A full rewire with certificates adds to the value of your home which is the way the HSBC bank manager saw it too.
 
If you do go for the rewire - just make sure you write a specification for what you want now and possible future upgrades.

Talk it through with sparks who come to quote

Think about CAT 5 or 6 to rooms with TV's, aerial cables, boiler control wiring, mains smoke and heat alarms, outside lights and power .....

Adding things later could be major upheaval, more plastering and decorating and higher costs

Rewires, new circuits and changes in bathrooms fall under Part P of the building regs - so make sure the person doing the work provides electrical certificates AND Part P certificates too.
 
If you have just bought a house, skimping on trying to keep an aged fuseboard is not a good idea, nor would it comply with the regs...
Agree regarding an aged fuse board, and a minor point but according to the op it's a single RCD plastic consumer unit, i wouldn't call it aged although the make, condition and size would affect matters. It would certainly comply with regs if the non RCD ways had rcd protection installed before the rewire as the current regs are not retrospective.
 
up here we don't have the advantage of thieving dockers on the thames selling off imported cable and accessories on the cheap.we have to buy from wholesalers.
It shows that you haven't been in London since the 1960's all the old warehouses are now posh flats and the old "docks" don't exist anymore (my Father use to spend time at the docks when getting his next contract for a run on a ship)

Your docks are still running though, I know the prices for scarp alloy wheels have crashed but you can still get LAP stuff from Screwfix for your rewire of a Coronation Street style house ;o))))))))

Only pulling your leg, you on the Diamond White/White Lightning already?
 
Agree regarding an aged fuse board, and a minor point but according to the op it's a single RCD plastic consumer unit, i wouldn't call it aged although the make, condition and size would affect matters. It would certainly comply with regs if the non RCD ways had rcd protection installed before the rewire as the current regs are not retrospective.

But nobody in their right mind would keep an up front RCD board - unless they come to work on a horse.
 
Only pulling your leg, you on the Diamond White/White Lightning already?

never touch that rotgut. Theakstons Old Peculier when I can get it. Occasional cider is Old Rosie.
 
Thanks for all the replies, I'm going to try get a full rewire for 3 grand it's a three story two bed. we only bought it to do it up, so hopefully it will help when we come to sell it in 2 years time. It seems to be a busy time for sparks at the moment, can't seem to get any one round.
 
If you do go for the rewire - just make sure you write a specification for what you want now and possible future upgrades.

Talk it through with sparks who come to quote

Think about CAT 5 or 6 to rooms with TV's, aerial cables, boiler control wiring, mains smoke and heat alarms, outside lights and power .....

Adding things later could be major upheaval, more plastering and decorating and higher costs

Rewires, new circuits and changes in bathrooms fall under Part P of the building regs - so make sure the person doing the work provides electrical certificates AND Part P certificates too.

Excellent advice, I'm an electrical designer by trade so I'm just going to whip up a cad plan to price from.

Thanks again
 
I had an electrical spec' e mailed to me for a self build bungalow with detached garage to price up last week. From a retired chap, 63 pages with every ceiling and wall of every room on a seperate page ! :)
 
I had an electrical spec' e mailed to me for a self build bungalow with detached garage to price up last week. From a retired chap, 63 pages with every ceiling and wall of every room on a seperate page ! :)
I'd run away as you know he'll be looking over your shoulder day in day ut then will deduct the tea, biscuits and toilet paper consumed from the fan bill, I bet he also want the scrap cable..........
 
But nobody in their right mind would keep an up front RCD board - unless they come to work on a horse.
Pardon my ignorance, what's so wrong with an single RCD board - I know it's ideal to have a dual to stop everything going in the event of a current imbalance. Also, the meaning of an upfront board?

Cjeers
 
Pardon my ignorance, what's so wrong with an single RCD board - I know it's ideal to have a dual to stop everything going in the event of a current imbalance. Also, the meaning of an upfront board?

Cjeers
section 314."division of installation" (BS7671 17th ed.)
 
Thanks for all the replies, I'm going to try get a full rewire for 3 grand it's a three story two bed. we only bought it to do it up, so hopefully it will help when we come to sell it in 2 years time. It seems to be a busy time for sparks at the moment, can't seem to get any one round.
Maybe you can't seem to get anyone round because of your plans to get it done for 3 grand?
 
Pardon my ignorance, what's so wrong with an single RCD board - I know it's ideal to have a dual to stop everything going in the event of a current imbalance. Also, the meaning of an upfront board?

Cjeers

A full rewire would include an AMD 3 compliant fuseboard with 2 or more rcds
 
This is often the problem when the customer tries to dictate how much it should cost.

You'd be better to have a spec of what you need and want and let the spark give you a quote. Rather than telling them how much you think it should cost.

When I go to quote a job and the customer is telling me how much it should cost and keep going on about it, I tell them they have got the wrong person. I'll give them a quote, not the other way around.
 
Maybe the op should view threads about poor installations before setting an unrealistic budget for a rewire.

Write a spec and get at least 3 quotes ....
 
I haven't told any contractor the price I'm wanting, I've done exactly the above message got a spec and I'm getting them to tender it. The main struggle has been getting people round to quote and actually turn ip, last week may have just been a busy week as I've got 3 sparks coming round this week.

Cheers all
 
I haven't told any contractor the price I'm wanting, I've done exactly the above message got a spec and I'm getting them to tender it. The main struggle has been getting people round to quote and actually turn ip, last week may have just been a busy week as I've got 3 sparks coming round this week.

Cheers all

Don't think its been mentioned yet, will you be living in your property whilst rewire is being carried out? Will furniture need to be moved, and carpets & floor coverings?

If you can vacate the property, and there's nothing to move about, it will be cheaper than a lived in rewire. Not to mention all the dust & ----.

Go on holiday for a week. :)
 
I'm old fashioned just use the blank side of the yearly tax return and a pencil..........
the inside of a smoke alarm box has saved me numerous times ive been caught short without my notepad


if you hand me something that can be written on, ill write on it
 

Reply to Rewiring 40-50 year old wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
875
Looking for some advice and timescale here. I'm not an electrician just a tennet with a housing association. I've been offered top floor flat in a...
Replies
6
Views
509
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hello, Last year I had some electrical work completed in my house (New CU, SWA for garage, downlights) I informed the electrician that I will be...
Replies
8
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
771

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock