The conduit can still be used as the CPC as long a suitable flylead is connected. There were, and still are suitable conduit fittings for connecting a fly lead to a conduit.

I realise they weren't available in the past but these days I use the piranha nuts on the end of steel conduit if I'm running it in to an insulated enclosure .
Sorry Dave you are saying that if the conduit is not connected into the box (if it's wooden) then use a connection via a flying lead connected to the conduit, that would be a tad difficult with the tube being buried in the plaster, don't you think? good idea though.
 
Also, you would need to know if there is a CPC serving the length of the ring final circuit, which as there's no earth conductor and wooden boxes I would highly doubt it. Again though, this needs to be ascertained through the correct test procedures.
It's in steel conduit, therefore there must be a cpc at every point already
I do know without seeing it, but there are a few different ways. There is such a thing as a coupler with a terminal fixed to the outside which is used to connect a flylead to the conduit.

You've told me that because it's in a steel conduit it must have a CPC at every point. Then you've told ne, when I asked how continuity was achieved that you don't know without seeing it.

So which is it?
 
Battle of the Dave sparks, who will win, only one way to find out....FIIIIIIIGGGGGHHHHTTTT:handfist::handfist::handfist::handfist::handfist:
 
Its all pointless! Until we have more detail there is no right or wrong advise to give regarding the condition of the installation.

To the O.P

As already mentioned - get a reputable electrician in to do a proper inspection and test. Then come back to us with his/her detailed report.
 
Sorry Dave you are saying that if the conduit is not connected into the box (if it's wooden) then use a connection via a flying lead connected to the conduit, that would be a tad difficult with the tube being buried in the plaster, don't you think? good idea though.

No, I'm saying that there are ways the original installers could have made the connections to a fly lead
 

Reply to rewiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
720
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
898
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi What would be your thoughts on this one? I bought this property last year, it was rented since 2005. EICR from 2016 states "wiring in fairly...
Replies
14
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
866

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock