Why would you us a ring for this? Dedicated circuits for heavy appliances are normally better off installed as radials.
A ring serving only heavy appliances may be the better solution. And a cheaper solution if say using AFDDs. Then only one needs to be used.

Three radials say with expensive AFDDs or RCBO's, can be quite expensive for no to little gain over a ring.
 
A ring serving only heavy appliances may be the better solution. And a cheaper solution if say using AFDDs. Then only one needs to be used.

Three radials say with expensive AFDDs or RCBO's, can be quite expensive for no to little gain over a ring.

Better in what regard?

Certainly not in terms of dealing with earth leakage, where 30mA protection is mandated at source. At the present time, there's no requirent to fit AFDDs for circuits suppling applainces, in the vast majority of domestic installations, so their realtively high cost (for now) is of little consequence.
 
A ring serving only heavy appliances may be the better solution. And a cheaper solution if say using AFDDs. Then only one needs to be used.

Three radials say with expensive AFDDs or RCBO's, can be quite expensive for no to little gain over a ring.

You're just turning this into the thread that was closed last week.
 
Because it works 24/7/365, drawing a fair bit of amps. Sockets were not intended or designed for such permanent use. No one would wire a 3kW immersion on a 13A socket. I have seen large fridge sockets get brown with heat.

If a plug and socket have a problem with 750 Watts then you haven't fitted them properly.
 
Last edited by a moderator:
Because it works 24/7/365, drawing a fair bit of amps. Sockets were not intended or designed for such permanent use. No one would wire a 3kW immersion on a 13A socket. I have seen large fridge sockets get brown with heat.

'Drawing a fair bit of amps' at 750W? 3.26A to be precise.

No one would place a 3kW immersion heater on a 13A socket because doing so would involve terrible design, exceed its 13A rating and also would be out of step with the regulatory reccomendation that all fixed loads over 2kW be placed on their own dedicated circuit.

As such, any comparision between a 750W fridge and 3kW immersion heater is pointless.

Would you consider powering a 3kW immersion heater from your theoretical 'ring final busbar'?
 
Last edited:
A ring serving only heavy appliances may be the better solution. And a cheaper solution if say using AFDDs. Then only one needs to be used.

Three radials say with expensive AFDDs or RCBO's, can be quite expensive for no to little gain over a ring.

Why has one appliance circuit suddenly become 3? You're moving the goal posts to suit your point.

Yes of course 1 circuit is cheaper to install than 3, that's pretty obvious.
 
No one would wire a 3kW immersion on a 13A socket.

As a temporary measure most people will do exactly that, but no you wouldn't normally as a permanent connection.

But an immersion heater is very different to a fridge.
A fridge is a stand-alone appliance, supplied with a flexible cable and plug and is intended to be connected by that cable and plug.
An immersion heater is a component to be installed into a larger system, it is supplied without any cable or plug and is designed to be connected, by whatever means is appropriate, by whoever assembles that larger system.
There's nothing to say that immersion heater can't be connected by a plug and socket, but I think most of us would be more likely to use a 15A or 16A socket rather than a 13A one.

I have seen large fridge sockets get brown with heat.

We've all seen sockets burned out. Not that long ago I had to replace a 63A socket which had completely burned out and had a plug stuck in it. This doesn't prove anything.
 
You inferred that a 750W fridge was the cause of thermal damage to a socket, whereas the response pointed out that other factors were much more likely to have caused the damage - factors which aren't removed by hardwiring an appliance.
Hard wiring a permanently connected appliance, rather than permantly plugged into a portable appliance outlet, make matters safer.
 
Hard wiring a permanently connected appliance, rather than permantly plugged into a portable appliance outlet, make matters safer.

Perhaps you could expand upon this as I fail to understand how a 750W fridge is 'made safer' by hardwirng through an outlet plate, than connected via a BS1363 plug/socket arrangement.
 
Perhaps you could expand upon this as I fail to understand how a 750W fridge is 'made safer' by hardwirng through an outlet plate, than connected via a BS1363 plug/socket arrangement.


It is obviously far safer for a homeowner who has bought a new fridge to cut off a factory fitted plug and connect the flex into an outlet plate, having been to a wholesaler and purchased 3 individual ferrules, than it is for them to plug it in to a socket!

Those rules they brought in about all new domestic appliances being supplied with a plug fitted to them were obviously pointless, they days of people having to fit their onw plugs to everything we're far safer.
 
Hard wiring a permanently connected appliance, rather than permantly plugged into a portable appliance outlet, make matters safer.

What is a 'portable appliance outlet'? You can't just change the name or definition of a socket outlet to suit your argument!

If hardwiring of domestic appliances made things safer then the rules wouldn't have been changed to require all appliances suitable for connection by a 13A plug to be supplied with one fitted!
 
I used to believe this too. I don't know if it was included in the 15th or 16th edition, but there's no mention of it in BS7671:2018+Amd2:2022 (at least as far as I can see).

Drew a blank in BBB, but H2.4 of new OSG is clear on this point:

"....the number of non-fused spurs should not exceed the total number of socket outlets and items of stationary equipment connected directly in the circuit".

As such the number of sockets isn't the issue, but the number of points connected directly to the ring.
 
Yep. A socket is a socket.

So, a 110v yellow socket is the same as a blue 230v commando socket which therefore is also the same as a bs1363? Bugger, I've been doing it wrong for so long.....
 
The back box is a dual backbox slightly wider than a standard double back box allowing 2 single face plates to be fitted, be they single socket outlet, flex outlet or FCU.
Or you could use one of these
1668371492361.png

And have a double socket and a spur
 
Just thinking about every point being a spur off the rfc, and no actual points as part of the rfc…..

What if you want to add an additional socket or point next to an existing?
You would have to go to the joint box rather than a local socket.
 

Reply to Ring Final Circuit - spurs only in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
789
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
262
Grateful if someone could offer some advise, I'm struggling to find a definitive answer to this. I have a double socket, it was on the ring main...
Replies
8
Views
764

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock