It's a hypothetical question..
32a Mcb is overrated for a 2.5 radial, but chuck a couple of cables in and suddenly it's okay..

A 32A MCB is overrated for a radial circuit run in 2.5 but it is not incorrect for one double (or single) socket outlet on 2.5.
Because the nature of the load is such that you cannot have an overload as the socket outlets will use fused plugs that limit the maximum current.

So where there is a situation where there cannot be an overload there is no requirement to provide overload protection, only fault protection and the MCB will provide fault protection.

In your example having a single spur off the MCB for a ring and then removing the ring would be still compliant with the regulations, however you would not be able to add outlets to this (now) radial.
 
A 32A MCB is overrated for a radial circuit run in 2.5 but it is not incorrect for one double (or single) socket outlet on 2.5.
Because the nature of the load is such that you cannot have an overload as the socket outlets will use fused plugs that limit the maximum current.

So where there is a situation where there cannot be an overload there is no requirement to provide overload protection, only fault protection and the MCB will provide fault protection.

In your example having a single spur off the MCB for a ring and then removing the ring would be still compliant with the regulations, however you would not be able to add outlets to this (now) radial.

Okay I see your point now.

Thanks.
 
are you not doubling your csa with a ring making the load you can draw off it higher hence 32a mcb does this not make the ring better for handling more load being drawn off any socket on it ?
 
New posts

Reply to Ring vs Radial in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock