Discuss Running 10mm T+E under celler joists. in the UK Electrical Forum area at ElectriciansForums.net

I'm struggling to picture this to be honest. Any chance of photos?

And again, does the routing of the cable comply with it not being RCD protected?

Not positive but I think the fact that the cable will be visible after exit from the bottom of the CU stud wall permits Non RCD? If taking the
T/E to SWA approach, yes the SWA length would be buried, but this part would be to spec as directed by a contracted electrician.
It is not intended that any of the 10mmm T/E will be embedded at any point, say in masonry (except when it passes into the garden directly through the cellar wall).
 
My advice is to forget about the T&E and just install a conduit with draw wire in the wall so that the SWA can be pulled in to it when it is installed thus avoiding any joints in a new circuit.
Th conduit would need to come out if the wall below the CU to allow fitting of the gland but could be covered with a blank plate for now.

Thanks davesparks (and thanks Archy Styrigg). Draw wire sounds like a good approach.

If I understand correctly I would need to leave a pull wire through an appropriately sized hole in the Stud Wall foot plate. The hole would need to be large enough to accept the diameter of the SWA.

There are no noggins below the Consumer Unit, so perhaps no need for a temporary conduit, if this is what you meant.

The only problem is that the Noggin at the height of the consumer unit. As well as supporting the consumer unit, it helps to support the weight of the cables exiting the back of the CU before dropping down. But then it also narrows and impedes the route into the back of the CU.
I think regardless of any conduit it will make it difficult for the electrician to pull in the SWA.

However I imagine that it might be possible with the main fuse switched off to temporarily unscrew the whole of the CU and pull it away enough from the wall to enable a cable to be pulled up and worked through the back. Just guessing. Perhaps electricians have other standard tricks to overcome this particular
issue.

Tricky, but it would be great to have the whole run in SWA and installed by an electrician. Let me off the hook? Food for thought.

I investigated a socket today feeding the boiler. It was 1.5 T/E. But could not find a corresponding FCU anywhere to correspond.
From the cellar I could see two 2.5 T/E main loop cables disappearing up into masonry but on the wall a single 1.5 T/E. It had been doing my head in for a few days.
I brought in a wire detector to try and trace. Was not sure if the detector would be any good through masonry (very cheap unit I bought years ago).
The 2.5 T/E were buried JUST beneath the surface of a separate of a adjoining wall and were picked up by the detector. No question of Permitted Zones here!

Chiseled out the 2.5 T/E in its plastic sheathing up to a standard 30Amp junction box, where it output 1.5 T/E round the corner.
The tough plastic junction box even had metallic plates plastered in front. But the hidden cables dropping down, hidden just beneath the surface, just begging for a nail was.. well Shocking!
Was this ok practice in the 80's when the original conversion I believe took place?

This is the third Hidden electrical outlet I have found! But the worst so far.

Thanks to all.
 

Reply to Running 10mm T+E under celler joists. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Replies
11
Views
573
Hi, I have two questions about domestic wiring In Ireland 1. Should conduit be used when passing multiple T&E cables (2.5mm) through a garage...
Replies
6
Views
795
  • Question
Hi All. I need to extend the cables for a 3 plate ceiling rose/pendant on ground floor ceiling by 450mm. Can I fix the ceiling rose/pendant to...
Replies
5
Views
365
I would like to run power to a shed that is 40m from my other shed which is powered by a 10mm cable from the house. I have access to a 100m roll...
Replies
3
Views
957
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock