Thanks, I did a bunch of digging and came to the same conclusion. The #10 is right on the edge considering ambient temperature and proximity to the roof surface. The nec can be confusing, refer to such and such, which refers you to such and such and so on.

According to emt and liquidtight fill charts I could put the 3 required #8 wires in 1/2" conduit. Did I miss something?

Not a top fed panel, going to tape over the feeds to the main breaker before getting to work in there.

During my research, it also seems that I have to use wire rated for wet locations, even though it is in conduit. Thwn or thwn-2? I could swear we were using thhn when I was doing solar installation back in the day.

You are saying the wire has to be continuous or the conduit type? Also, I was under the impression that romex was prohibited on such a circumstance.
Thanks, I did a bunch of digging and came to the same conclusion. The #10 is right on the edge considering ambient temperature and proximity to the roof surface. The nec can be confusing, refer to such and such, which refers you to such and such and so on.

According to emt and liquidtight fill charts I could put the 3 required #8 wires in 1/2" conduit. Did I miss something?

Not a top fed panel, going to tape over the feeds to the main breaker before getting to work in there.

During my research, it also seems that I have to use wire rated for wet locations, even though it is in conduit. Thwn or thwn-2? I could swear we were using thhn when I was doing solar installation back in the day.

You are saying the wire has to be continuous or the conduit type? Also, I was under the impression that romex was prohibited on such a circumstance.
If it’s a home you are working on then you can use romex but since you are putting it in pipe and using THHN or THWN is designed for wet locations. Yes you can use 1/2 pipe but it would be a hard pull. My advice is to use 3/4 pipe and the wire can be spliced but the raceway has to be continuous.
 

Reply to Running new circuit to AC unit, please review my plan. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
Installing exterior outlet running off new 20 amp gfci breaker. I have a good understanding of the outdoor section of the circuit as well as...
Replies
1
Views
1K
First thanks in advance I have question about a ac unit. I replaced a window unit that was wired for 240 with a 20 amp plug. New unit is 240 with...
Replies
1
Views
1K
At my new lake house, I'm planning to rebuild an unattached shed and make it a Shed/Bunkhouse combo. The current wiring to the existing shed...
Replies
1
Views
1K
My Current Setup (see image BEFORE.jpg): The wiring for my existing detached garage is shown (see image BEFORE.jpg). The house consumer unit...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock