First thanks in advance
I have question about a ac unit. I replaced a window unit that was wired for 240 with a 20 amp plug. New unit is 240 with a 30 amp plug. Checked the wire that was installed and its 12 awg so I didnt want to run a 30 amp breaker on that 12 awg. I installed the 30 plug on the 12 awg but left the 20 amp breaker in the box. My thought was if the unit pulls more then 20 amps it should trip correct? I started the unit (its brand new 28,000 btu) and it runs like a top. The side panel on the unit says 13.5/15.0 amps. Is this ok for a short time until I can get someone out to replace the 12 awg with 10 awg and install the 30 amp breaker? I dont plan to run it much but we are going through a hot spell for a couple days. Am I safe to assume it wont overload the wire since I left the 20 amp breaker in the box? This wire is dedicated to only the ac unit

Thank you very much
Terry
 
First thanks in advance
I have question about a ac unit. I replaced a window unit that was wired for 240 with a 20 amp plug. New unit is 240 with a 30 amp plug. Checked the wire that was installed and its 12 awg so I didnt want to run a 30 amp breaker on that 12 awg. I installed the 30 plug on the 12 awg but left the 20 amp breaker in the box. My thought was if the unit pulls more then 20 amps it should trip correct? I started the unit (its brand new 28,000 btu) and it runs like a top. The side panel on the unit says 13.5/15.0 amps. Is this ok for a short time until I can get someone out to replace the 12 awg with 10 awg and install the 30 amp breaker? I dont plan to run it much but we are going through a hot spell for a couple days. Am I safe to assume it wont overload the wire since I left the 20 amp breaker in the box? This wire is dedicated to only the ac unit

Thank you very much
Terry
Terry please don’t run that AC very much because it take a lot of power for the compressor when it kicks off and on the breaker might not be tripping right now you are causing heat in the wire and receptacle because I bet you the actual receptacle is just rated for 15 amps. If you must run foot for short periods of time and feel the receptacle to see if it getting warm. Be careful that could cause a fire.
 

Reply to Window ac unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
826
I bought this house a couple months ago. It was built in 1952 (same as me) but has been rewired with yellow 12 awg Romex dated 2007. Looks like a...
Replies
7
Views
520
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
469
I may have posted this before but not sure if it made it in. I want to install an EV Charger in my garage. The panel is two stories up and the...
Replies
0
Views
489
I’m planning a 240V welder circuit in a detached garage with a 100A sub panel. For the 160A or 180A output welders I’m looking at, the conductor...
Replies
5
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock