seprim

Hi
I am not yet MCS but I have C&G2372 and I am a little rusty :eek: , and have designed a system using currently available gear. The design is as follows;
16 Sanyo HIT250's
SB4000TL
Arranged in 2 strings of 8 modules in each string
Assumptions
1. My first assumption is that as its ≤4KW that it complies with FIT rules and as such would attract the highest rate, because 16 x 250Wp = 4KWp. . . .
2. Secondly that the PV panels and Inverter are compatible because in two seperate strings of 8 modules I have maximum DC voltage = Voc x 8 = 43.1 x 8 = 344.8v (which is a good deal less than the 550v stated as max for the inverter)
3. and that String mpp voltage for each of the strings is Vmpp x 8 = 34.9 x 8 = 279.2v which is less than the inverter max dc voltage and also, quite usefully i think - nearly half way between the min and max of the range given for the inverter's MPP voltage range (175v - 440v) mid way being 307.5v hence a difference of 307.5 - 279.2 = 28.3v [~10% out of dead centre]
4. also that the module Isc (7.74A) would show an array Isc of 15.48 A which is less than the maximum input current of 30A (2 strings of 15 A each)
5. peak power would be String mpp Voltage x Array mpp Current = 279.2v x 15.48A = 4,322.016 Watts . . and herein lies a dilemma - which do I use, Peak Power or Wp ? :confused:

Questions:
1. The SB4000TL has a maximum dc power of 4200W, yet my max output on a sunny winters day may well be 4322W . .. I was taught that generally the pv peak power is ~20% greater than the Inverter peak power. Would this design disqualify this installation from the ≤4KW FIT payment rate ? Would the DNO "have a baby" over this ?
2. Would I have to go G59/2-1 rather than G83/1-1 ? and would that alone disqualify the design from FIT ? :confused:
3. If i chose a different module, say HIT240's and the array peak power would be 3.85kW. Ignoring losses thats 16.75A put back into the grid. This is over the DNO stipulated maximum for G83/1-1 but less than the FIT repayment limit. . . would the DNO allow this arrangement ? Are they flexible ?
5. Has anyone had to do this to maximise the output and hence FIT for a customer ?
6. Why has the DNO stipulated a maximum in current (Amps) and the FIT's stipulated the maximum in power (Watts) ? Are they not singing from the same sheet ? :confused:

Andy
thx, and stay frosty :cool:
 
Hi
I am not yet MCS but I have C&G2372 and I am a little rusty :eek: , and have designed a system using currently available gear. The design is as follows;
16 Sanyo HIT250's
SB4000TL
Arranged in 2 strings of 8 modules in each string
Assumptions
1. My first assumption is that as its ≤4KW that it complies with FIT rules and as such would attract the highest rate, because 16 x 250Wp = 4KWp. . . .
2. Secondly that the PV panels and Inverter are compatible because in two seperate strings of 8 modules I have maximum DC voltage = Voc x 8 = 43.1 x 8 = 344.8v (which is a good deal less than the 550v stated as max for the inverter)
3. and that String mpp voltage for each of the strings is Vmpp x 8 = 34.9 x 8 = 279.2v which is less than the inverter max dc voltage and also, quite usefully i think - nearly half way between the min and max of the range given for the inverter's MPP voltage range (175v - 440v) mid way being 307.5v hence a difference of 307.5 - 279.2 = 28.3v [~10% out of dead centre]
4. also that the module Isc (7.74A) would show an array Isc of 15.48 A which is less than the maximum input current of 30A (2 strings of 15 A each)
5. peak power would be String mpp Voltage x Array mpp Current = 279.2v x 15.48A = 4,322.016 Watts . . and herein lies a dilemma - which do I use, Peak Power or Wp ? :confused:

Questions:
1. The SB4000TL has a maximum dc power of 4200W, yet my max output on a sunny winters day may well be 4322W . .. I was taught that generally the pv peak power is ~20% greater than the Inverter peak power. Would this design disqualify this installation from the ≤4KW FIT payment rate ? Would the DNO "have a baby" over this ?
2. Would I have to go G59/2-1 rather than G83/1-1 ? and would that alone disqualify the design from FIT ? :confused:
3. If i chose a different module, say HIT240's and the array peak power would be 3.85kW. Ignoring losses thats 16.75A put back into the grid. This is over the DNO stipulated maximum for G83/1-1 but less than the FIT repayment limit. . . would the DNO allow this arrangement ? Are they flexible ?
5. Has anyone had to do this to maximise the output and hence FIT for a customer ?
6. Why has the DNO stipulated a maximum in current (Amps) and the FIT's stipulated the maximum in power (Watts) ? Are they not singing from the same sheet ? :confused:

Andy
thx, and stay frosty :cool:

Run it through SMA free software its very easy to use and effective.
 
Hi
I have been in touch with my DNO (UK PowerNetworks) and been sent some useful info, clarifying a whole load of stuff that I have asked in this post. It didn't answer all my questions but I must give my brain some time to absorb the info and apply common sense to it ;)
Here goes;
Assumptions:
My first assumption that the DNO is interested in the DC output of the panels is false. They are only interested in the AC output of the system. To comply with G83/1-1 this must not exceed 16 amps @ 240volts (yes 240) = 3.86kW. - read on . . .

calculations assumptions - no further info qualifying or denying these calculations
Is Wp peak power ? No - Peak power according to the DNO is the “AC output” = no. modules x Wp x efficiency of inverter = 16 x 250 x 97% = 3.88kW so this arrangement would not be acceptable for G83/1-1 according to this DNO.
NOTE: if I used HIT245's instead of HIT250's then the “AC output” would be as follows – 16 x 245 x 97% = 3.8024kW which is below the 3.86kW threshold and hence acceptable to this DNO for G83/1-1.

Questions:
Essentially I think the question here is . . can I use an SB4000TL ? And the answer is yes, you can, according to this DNO (at least they have no problems with it) because it has a G83 Compliance Certificate, and;
The DNO require you to compare the AC output of the system with the rated output of the inverter, and then use the smaller of the two.
e.g. SB4000TL rated AC output = 4000W and if the max AC output from the array and inverter is 3.8024kW (if HIT245's are used). One would use 3.8024kW (the lesser of two weevils).
So would this design (originally 16 no. HIT250's and an SB400TL) disqualify this installation from the ≤4KW FIT payment rate ? - No
Would the DNO "have a baby" over this ? - No :) because for this DNO, one would have to apply for permission to connect a 3.84kW ≤ Output ≤ 4kW generation, making it plain that it is for a single installation, and it must be accompanied by a location map.
No G59 is required with this design and No it wouldn't disqualify from FIT (with this DNO)
Could I use HIT240's – Yes. NOTE When applying for permission it is advisable that one applies as soon as possible as commissioning depends on permission and this may take some time . . . .Could the DNO refuse permission in some areas ? Yes . .perhaps, but I don't know for sure.

Has anyone had to do this ? The question remains. .

Why has the DNO stipulated a maximum in current (Amps) and the FIT's stipulated the maximum in power (Watts) ? - Still don't know that one :)
My Caveat would be - if you have a 3.84kW ≤ Output ≤ 4kW SSEG design and you want to know if you can install it - contact your DNO first ;)
Regards

Andrew - stay frosty:cool:
 
Hi Andrew,
Thanks for this really useful post; I'm in exactly the same situation - 1st PV install since training in April, same proposed system config and same DNO (I'm in Mid Sussex, nr East Grinstead) so this stuff is a god send for me!
BTW, where are you getting your kit from? Been spending a lot of time doing a lot of research on suitable trade suppliers.
Have you done the install yet? Would be interested to know how it went!
Cheers,
Vaughn.
 
Hi Vaughn
I am in the process of doing my first install. I got a kit from CEF, although if you search on "suppliers" in this forum you will get lots of company details as well as feedback on their performance from individuals experiences. The install took me a week on my jack and as I was new to roofs i went pretty carefully. (also cos i weigh 18 stone and could have broken all the tiles but i only eventually broke 6)
I have my inspection soon (although no date confirmed yet as I am sorting out the QMS right now) I will let you know how it went
Andrew :ninja:
 
Thanks for the update, and good luck with the inspection! Hope it goes well!
How are you doing your QMS - r u going thro EasyMCS or something similar?
 
This is where the confusion starts 230, or 240. Unfortunately you are at the mercy of the DNO as to what they will accept. Been talking to SPN who basically said they were fed up waiting for clarification on the matter and have set their own rules.

Done a couple of SMA 4000TL's and had to complete a G83 stage 2 application and have not had a problem yet. The guide does state to get in touch with your DNO early in the process..........best to get them onside from day 1....

As to the installs, all I had to do was shift the frequence cut out to 51.5Hz at 5 secs. You will need to contact SMA to get your Gridguard access code to modify the settings though. I then had to take a screen shot ( Sunny Explorer) showing the changes to be submitted as part of the connection confirmation.
 
Hi yellowvanman - that was my first thought but the DNO specifically said 16A @ 240V, so I asked "are you sure" and the DNO said yes absolutely so.
I quote
"The first point to note is that G83 has a fixed upper limit of 16 Amps per phase at 240 Volts (3.84kW), which doesn't quite extend to the 4kW of the first band of the Feed-In Tariff. However, many installers, in talking to customers, who want to hear a big number, refer to the size of the installation according to the DC output of the Solar Panels, whereas we as a Distribution Network Operator, are concerned with the AC Output from the inverter. Please see the explanation below on how to calculate the output to record on the G83 form.
Calculation of the size of the SSEG
Some installers appeared to mis-understand the rating of the SSEG as it should be reported on the G83 form. What is required is the maximum output from the SSEG, not the total rating of the solar panels. The calculation should be done, as follows:
Add the total rating of all of the solar panels. Call this SP_Rating.
Identify the efficiency of the inverter. Some inverters have charts showing how the efficiency varies with the DC Input Voltage, and other factors, and some just state an 'Average Efficiency'. Call this Inverter_Efficiency.
Multiply the two figures (i.e. SP_Rating x Inverter_Efficiency). Call this Output_1.
Compare Output_1 with the maximum rated output of the Inverter. Take the smaller figure. This is the SSEG output which should be reported.
Consider the following worked example:
7 solar panels rated at 235 Watts each, with a Sunny Boy 1200, (rated at 1200 Watts)
7 x 235 = 1645 Watts (SP_Rating)
Inverter Efficiency = 92% (Inverter_Efficiency).
SP_Rating x Inverter_Efficiency = Output_1.
1645 x 92% = 1513.4 Watts (Output_1)
Compare Output_1 (1513.4 Watts) with the rated output of the Sunny Boy 1200 (1200 Watts), and take the smaller figure, which is 1200 Watts.

Generation up to 3.84kW Per Phase
You need to note that G83 allows for up to 16 Amps per phase at 240V AC (i.e. 3.84kW), and there is no flexibility to exceed 16 Amps per phase under G83.

Submitting G83 Notifications
The G83 form needs to be accompanied by a copy of the G83 Compliance certificate of the Inverter and a Schematic Diagram of the installation.
Our preferred method of receiving G83 registrations is by email to the address on the form. When G83 Registrations are made by email, it is sufficient to type your name as your signature.

MPANs
A key item of information for the registration is the MPAN, which is on the Customer's electricity bill. Experienced installers collect this information when the customer places the order.
There is a useful webpage to identify the DNO from the MPAN at:
Meter Point Administration Number - Wikipedia, the free encyclopedia

Generation between 3.84kW and 4.00kW Per Phase
If you are considering an installation which is between 3.84 and 4kW, then you will need to Apply for permission to connect this generation. Please complete our G83 Application form, making plain that this is for a single installation, and send it to the email address or the Fax number:
Email: [email protected] Fax: 08456 500248
The Application from is available at:
http://www.ukpowernetworks.co.uk/pr...83_multiple_installation_application_form.doc
The application needs to be accompanied by a Location Map.

Larger Generation
For larger generation, please contact me again for guidance on how to connect generation which is in excess of 4kW per phase."
. . .end quote
It doesnt explain why they still use 240V as opposed to 230V but the other info may be useful.
regards

Andrew
 
Hi
You best apply for a grid guard code from SMA so that you can set the Pmax limit to 3.68 so that it wont output more then the 16A under G83

good luck
 
When you install the SMA 4000TL, under "country data set" for England it specifies G83/1. Does that automatically limit it to below 16A? I see that under "grid guard protection" it says No. What does that mean?
 
When you install the SMA 4000TL, under "country data set" for England it specifies G83/1. Does that automatically limit it to below 16A? I see that under "grid guard protection" it says No. What does that mean?

There is a host of information on SMA's website, also have you tried searching this forum for 'Grid Guard', there is a host of information here also. Check out threads relating to G83, overpowering an inverter etc.




Am I getting groachy? :90:
 
Last edited:
My DNO says having had similar discussions in the past that re SMA 4000TL and 4kW array

"The issue of G83 installations where we think there may be problems if less than 16A per phase systems are installed without prior reference to us has been batted around between various people within our organisation. The outcome is that, for systems of up to 4kW single phase (or 12kW three phase), we will permit connection without reference to us and that, should problems arise after commissioning W.P.D. will cover the cost of any rectification work needed. Proposed systems larger than this should be referred to us prior to installation so that we can assess the network. In these cases any reinforcement required would be chargeable to the customer."
 
@flamefix

Which part of WPD is that and can you post the actual email here please?

Thx
 
That is the whole email apart from headers and names but I can't post that.

This is the email footer.


Western Power Distribution (South West) plc / Western Power Distribution (South Wales) plc
Registered in England and Wales
Registered number: 2366894 (South West) / 2366985 (South Wales)
Registered Office: Avonbank, Feeder Road, Bristol, BS2 0TB
 
well send them the information here, I was losing business because I was originally told to check any install first (rural) because the problems with the line and current could mean the client would have to pay for an upgrade. I was forever back and forth, eventually that was the decision, after some argument on my part via and help the greenbuilding forum..

The agreement was given after the following conversation.

Question:
Can someone tell me, in simple terms, why putting say 20amps into the grid might cause more problems than taking 80 amps out of it? Afterall, it is alternating current so the current goes forwards and backwards in both cases.

Most of us have either an 80 or 100amp main fuse, These generally need either a prolonged current or a significant overload to blow them.


DNO's position:
Voltage fluctuations are a big deal for the DNO but also the end user. In periods of low demand the voltage rises, with an SSEG providing additional output the voltage can exceed the 253v this means the DNO breaks statutory limitations. Also the inverter senses an over voltage and drops out, the user then isn't generating and isn't earning FIT. Ergo two unhappy souls.
All installations are at the discretion of the DNO. It therefore follows it is the installers fault if an installation over 3.6kW is installed and the DNO says NO it can't be approved or you the client are asked to pay to upgrade the DNO's supply to accommodate your PV array(SSEG). Until that is done the array cannot earn FIT and is not approved.

However up to 3.6kW no one is at fault if the installation isn't approved by the DNO, if they refuse it on the grounds their supply can't accept it, because under the current arrangement the installer only needs to notify one day prior to connection and within 30 days. Therefore it is advisable that the DNO is notified prior to agreeing any array size because it may not be possible without additional expense.
I work in a rural and urban area, and rural are particularly prone to sizing restraints and often perfectly good roofs for 3.6kW are refused when I approach the DNO and limited to 1.5kW or 2.5kW for example, unless the DNO supply side is Upgraded.

Hence I was losing jobs because anyone not aware of this was quoting based on the the up to 4kW rule.
And it wasn't the current issue it was the Overvoltage problems they actually face.

Argument was presented based on the following:

The Electricity Safety, Quality and Continuity Regulations 2002 state:

Quote
(2) Sub-paragraphs (b) and (d) of paragraph (1) shall not apply to a person who installs or operates a source of energy which may be connected in parallel with a distributor’s network provided that sub-paragraphs (a) and (c) of paragraph (1) are complied with; and
(a) the source of energy does not produce an electrical output exceeding 16 amperes per phase at low voltage;
(b) the source of energy is configured to disconnect itself electrically from the parallel connection when the distributor’s equipment disconnects the supply of electricity to the person’s installation; and
(c) the person installing the source of energy ensures that the distributor is advised of the intention to use the source of energy in parallel with the network before, or at the time of, commissioning the source.

and the appropriate Explanatory Notes state:

Duty holders should note that equipment installers need only notify the local distributor, i.e. they do not need to ask permission to connect the equipment and regulation 22(2)(c) does not give distributors opportunity to refuse such equipment being connected.
This revocation of the need to notify is the whole reason why G83 exists and why 16A per phase has been selected as an acceptable threshold.

I know there is increasing concern amongst DNOs about the resilience of the network to installation of micro-generation.

I agree that there may be an issue with any <16A per phase installation - but if there is then it is up to the DNO to sort it out at their own expense, not anyone elses as the costs of handling this is covered in the DUOS element of everyone's electricity bills.
And if that happens then the DNO have been given the responsibility of fixing it and at their own expense - unless they can off-load the cost to some unlucky G59 "customer". The costs of doing this are already built in to every consumer's electricity bill. There is no way that any G83 system owner should be required to pay for any network upgrades even if the upgrade is required because of a multiple number of G83 systems in a small area.

But I can understand why DNOs, in these straightened financial times, are trying to wriggle around it.

The reasons DNOs will get upset are due to voltage level fluctuations, voltage unbalances across 3 phases and harmonics. None of these are really issues with individual SSEGs but will be due to aggregations from multiple SSEGs all in one area.

DNOs are empowered to disconnect people from the grid if they believe that the consumer has an unsafe installation or if they are responsible for causing interference to neighbours. But in the context of multiple SSEGs they would have to prove that the problem was attributable to specific individuals - whereas the issue would be that everyone with a SSEG was a small part of the larger problem and that a 'last in, first thrown out' approach would be very unlikely to stand up in court under appeal


Could you provide any enlightenment on the above, and cite where the DNO has the rights over and above the G83 notification process to charge the user for modifications to the network.



Following that:
I had the response I posted earlier and I think it is a very enlightened view.
 
Well what can I say.

Revised information on the above. DNO informs us that the max install capacity without referring to the DNO is now 3.68kW
 
Hi,

I have used a SB 4000TL on a 4kW system (YEDL) ..... although it does vary from DNO to DNO, the bottom line is (in my opinion), if it has a G83 certificate, it has to be accepted. In my case it was, without any comment.

Hope this helps
 

Reply to Sanyo HIT250's and SB4000TL in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top