Hello,

My current 2.5kW Solar pv array is in a less than favourable position, but there is plenty of space to expand the array. I have an additional 4kW of solar panels that I wish to add to the array as even during peak production we are lucky if we can achieve 1800W out of the 2.5kW so looking at overpowering the inverter.

Currently the array is connected to a SAJ 3600W inverter, but this has a max Vdc of 580V and Isc Max of 15A. If I overpower the inverter, from what I have read the max voltage must be adhered to, whereas the Isc can be over with parallel strings. (Solar panels have an Isc of 8.65A so will be over if I combine the strings.)

Alternatively I have a sunny boy 4000 inverter with two MPPTS, 2 x 15A. A quick question, does the Vdc max of the sunny boy get split between the two mppt (halving the max Vdc per string? Or are the two strings able to have 750v and the 15A each?
Thanks
 
You must always adhere to manufacturer specification. Specs will tell you max Vdc input from array, max Vdc per MPPT, max Isc and max recommended PV input power. With Isc you have to apply 1.25 factor to it as panel specs are given at standard test condition and at certain times they will generate more current then advertised. So for example if your string Isc is 10A then mppt Isc should be minimum 12.5A.
Looking at the specs of sunny boy, max input voltage is 750V which I would assume is for whole array as mppt voltage range is given at 175-500V. String voltage Does not have to be split 50/50 as long as you are within the range.
 

Reply to Overpowering solar inverter in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
678
Hello everyone, I currently have two solar modules left over from an installation and I would like to use them to set up a solar system on the...
Replies
3
Views
921
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
458
I thought I had an understanding of how to size an inverter but I think I have become slightly confused after taking to some proposed installers...
Replies
3
Views
2K
There are 2 inverters feeding into a dorman smith C16 rcbo , every time I visit this site (communal area power) it has tripped. it switches on...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock