Discuss max output from US 5000 pylontech batteries in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Tonyboy

DIY
Reaction score
18
Good morning all.

Before I start I am not an electrician and am relatively new to this topic.

Current set up Axpert 5.5 Kw inverter, 7 x 420 watt panels in series and 2 x US 5000 Pylontech batteries paired (1 master 1 slave). System working fine will no issues.

I know this may have a simple answer but I have worked through the manual and have done some calculations but to be sure I thought I would post this and get it for sure.

The manual for the batteries says max charge/discharge current 100 amps and recommended 80 amps for a battery. I won't be using anything like these figures but my question is this.

I want to be able to draw 3.5 Kw to 4 Kw from my batteries in the event the sun goes in and the panels stop producing power so I want to ensure the batteries will provide the power I require. So far I have been able to off set the battery draw with sunshine or daylight so the batteries have only really been drawing 2 to 2.4 Kw according to the bms.

I realise pairing 2 batteries gives me 200 amp hrs and another would make it 300 amp hrs etc and the voltage stays the same 48V but I am unsure how the max Kw output is calculated for two or more batteries. I was given to understand that 2 batteries would give me 2.4Kw output and adding another would give me 3.2 Kw etc but is this the case. I do not use that much power generally but I want to ensure I do not overdo it when using battery only.

Any help or a definitive reply would be very welcome

Regards

Tonyboy
 
Us5000 batteries have nominal voltage of 48v and nominal capacity of 4800W. Maximum charge discharge is 100A (4800W/48V) this is called 1C (your battery is charged/discharged from 0-100% or 100-0% in 1hr). You should avoid charging/discharging at 1C and use 0.5C which in this case is 50A(2400W/48V). You have 2 batteries in parallel so at 0.5C you can charge/discharge at 4800W or 100A.
If you add another battery that would be 7200W or 150A at 0.5C, however your inverter is rated at 5500W and that's max what it can provide.
Never discharge Your batteries to 0%, set depth of discharge in summer months to minimum of 10-15%.
In winter months you may need to increase it to something like 30-50% as there is not enough sun energy to charge them. Or it may be beneficial to disconnect 1 battery
 
Us5000 batteries have nominal voltage of 48v and nominal capacity of 4800W. Maximum charge discharge is 100A (4800W/48V) this is called 1C (your battery is charged/discharged from 0-100% or 100-0% in 1hr). You should avoid charging/discharging at 1C and use 0.5C which in this case is 50A(2400W/48V). You have 2 batteries in parallel so at 0.5C you can charge/discharge at 4800W or 100A.
If you add another battery that would be 7200W or 150A at 0.5C, however your inverter is rated at 5500W and that's max what it can provide.
Never discharge Your batteries to 0%, set depth of discharge in summer months to minimum of 10-15%.
In winter months you may need to increase it to something like 30-50% as there is not enough sun energy to charge them. Or it may be beneficial to disconnect 1 battery
Hello Kropaske and thanks for the reply.

I have my inverter setting 2 set to max 50 amp charge and a max of 10 amps charge on the standby utility power if I need it to charge overnight.

So from what I understand the setting 1C is the max for discharge and charge, and with my setting of 50 amps this would then be 0.5C as you indicated i.e. 2400w for one battery.

Therefore if I wish to charge/ discharge at 0.5c my present setup would mean at 0.5C then the Max would be 4800w but would this be limited by my setting the max charge to 50amps on the inverter and therefore reduce the charge/discharge to 2400w accordingly. (would it effectively be 0.25C ?) Would I then need to up the max charge discharge to 100amps to be able to charge/discharge 4800w from the pair of batteries?

I am planning to add at least one more battery but I am not wishing to use more than a nominal 3.5 to 4 Kw at any given time. My usage is quite low as it is a small house.

Hope this makes sense?

Regards

Tonyboy
 
Therefore if I wish to charge/ discharge at 0.5c my present setup would mean at 0.5C then the Max would be 4800w but would this be limited by my setting the max charge to 50amps on the inverter and therefore reduce the charge/discharge to 2400w accordingly. (would it effectively be 0.25C ?) Would I then need to up the max charge discharge to 100amps to be able to charge/discharge 4800w from the pair of batteries?
I don't know this inverter but if you set up correctly all the parameters (max voltages, capacity, etc) then inverter and battery bms should work out correct charging/discharging current. For example if you set total capacity at 4800W or 100Ah then charging/discharging at 0.5C would be 2400W but if you set total capacity at 9600W or 200Ah then at 0.5C you have 4800W
I am planning to add at least one more battery but I am not wishing to use more than a nominal 3.5 to 4 Kw at any given time. My usage is quite low as it is a small house.
If your usage is low what is the point of spending 1.5k on another battery. You have approx 3kwp system and you won't be able to fully charge those 3 batteries. On sunniest summer day you might generate around 16-18kwh but when winter come it will be 1-3kwh
 
I don't know this inverter but if you set up correctly all the parameters (max voltages, capacity, etc) then inverter and battery bms should work out correct charging/discharging current. For example if you set total capacity at 4800W or 100Ah then charging/discharging at 0.5C would be 2400W but if you set total capacity at 9600W or 200Ah then at 0.5C you have 4800W

If your usage is low what is the point of spending 1.5k on another battery. You have approx 3kwp system and you won't be able to fully charge those 3 batteries. On sunniest summer day you might generate around 16-18kwh but when winter come it will be 1-3kwh
Hi Again

I have got the capacity set to 9600w/200Ah already on the bms and the only thing I have adjusted is the max charge at 50 amps on the inverter.
I will try setting the inverter max to 100A, this would give the 0.5C rate for the 200 ah of batteries, I think my initial concern is that I am worried about drawing more than 4200kw through the system as shown on the bms as I did not know what this represented in terms of the amount the batteries can supply in the absence of the pv.

Maybe I am looking at things from the wrong perspective. I know the inverter will top out at 5.5 Kw and my intentions are to use no more than 4 to 4.5Kw at any one time. Given the inverter is best used at this sort of level for its long term good I have no problem doing so. As I said at the start I am not an electrician and some of the finer points of inverters and associated battery charging do need some explaining.

In respect of the additional battery, I see your point.
regards

Tonyboy
 

Reply to max output from US 5000 pylontech batteries in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have a basic knowledge of electric but would like advice before I attempt, I have a electrical item that is powered by Voltage...
Replies
2
Views
352
I thought I had an understanding of how to size an inverter but I think I have become slightly confused after taking to some proposed installers...
Replies
3
Views
2K
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
1
Views
437
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
645

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock