Discuss satisfactory unsatisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
7
Hi Guys.

If carrying out an EICR you are unable to find a UFH circuits spur, is the EICR still passable under some type of limitation? Or is there a code involved.

Thank you!

Smarky
 
You'd just mark it as FI and note why. However you'd also use your engineering judgment based on the condition of everything else as to whether you think it's likely to be an issue or not and issue satisfactory or unsatisfactory on that basis
 
You'd just mark it as FI and note why. However you'd also use your engineering judgment based on the condition of everything else as to whether you think it's likely to be an issue or not and issue satisfactory or unsatisfactory on that basis
Thanks for your quick response, Its greatly appreciated đź‘Ť
 
What exactly do you mean by can't find a spur?

Do you mean it's fed from a ring circuit but you can't find a switched fused connection unit or other means of fusing down and isolation for it?

If the UFH is connected directly to a ring circuit without a fuse of some kind then that's a C2 observation.

If its on a suitably sized dedicated circuit without an means of isolation other than the MCB then it is unlikely to warrant any code.
 
What exactly do you mean by can't find a spur?

Do you mean it's fed from a ring circuit but you can't find a switched fused connection unit or other means of fusing down and isolation for it?

If the UFH is connected directly to a ring circuit without a fuse of some kind then that's a C2 observation.

If its on a suitably sized dedicated circuit without an means of isolation other than the MCB then it is unlikely to warrant any code.
Hi Dave,

Thanks for your reply its on a dedicated circuit appropriately rated without a fused spur or at leaset unable to find one!
 
Hi Dave,

Thanks for your reply its on a dedicated circuit appropriately rated without a fused spur or at leaset unable to find one!
So basically you've just got a mystery cct where you know the start and what it's labelled for but can't locate the other end? Classic.
 
Why would a dedicated circuit need a fused connection unit?
Normally I would expect to see some sort of fused spur or at least if myself or the majority of people were to install such a circuit, then a fused spur would be put in - no!! or at least a point of connection to the UFH! Which i am unable to find.
 
Last edited:
Yes, a point of isolation would be very sensible, my question is more about why they would want a local fuse rather than just an isolator.
To be honest I just want an end to get a reading off! I said fused spur as that what I would normally see but some type of isolator or end of circuit to be able to get an r1 + r2 which i am currently unable to find.

Thanks

Smarky
 
Normally I would expect to see some sort of fused spur or at least if myself or the majority of people were to install such a circuit, then a fused spur would be put in - no!! or at least a point of connection to the UFH! Which i am unable to find.

I wouldnt expect to see a fused connection unit on a dedicated circuit, I'd expect to see an isolator. The MCB should be sized appropriately so a local fuse is unnecessary.

But you're not carrying out an EICR based on your opinion or exoectations, you are carrying it out based on the regulations.
As far as I know, and general consensus seems to be, that an MCB satisfies the minimum requirement as a means of isolating an appliance on a dedicated circuit.
 
You'd just mark it as FI and note why. However you'd also use your engineering judgment based on the condition of everything else as to whether you think it's likely to be an issue or not and issue satisfactory or unsatisfactory on that basis
"FI" automatically makes the Report outcome "Unsatisfactory".
 

Reply to satisfactory unsatisfactory in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall. Current carrying...
Replies
6
Views
970
Had an enquiry where the installation (commercial) is relatively new and client has requested a condition report. Probably 80-100 circuits plus...
Replies
8
Views
1K
Hi everybody, I've been asked to do a EICR in a commercial property, So i popped in to have a look on my way home quickly and found the lighting...
Replies
8
Views
462
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
856

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock