Hi all, not been on here for a while but ive had a strange problem today and wondered if anyone else has had it, i wired in a scame weatherproof switch, one switch controls a Sodium floodlight and the other a metal halide and a few fluorescents, i wired the led indicator lights one side to live and the other to switched live as i've done a hundred times before but when left for a while and you switch the lights on, they wont switch back off, its as if the switches are being magnetically held on, without the indicators connected they work fine no matter how long they're left, its a very strange one and i could do with finding out how to rectify it as you cant see where the switch is in the dark without them,cheers
 
when you say the led is wired live to switch live i wonder if current is passing through the LED from live to the switch live effectively shunting the switch. A simple check with test lamp will prove, Could you get a neutral to the switch to wire the LED live to neutral???
 
I think that is what is happening too, it got too dark and the guy was going out so i'll call back there tomorrow to check, getting a neutral there wouldnt be too much hardship just a length of 4core swa but i doubt the customer will bother with it to be honest, it switches off and on and doesnt electrocute him like the last switch so he's happy:lol:, its just odd because i've wired them like this before because of there being no neutral and they've been fine albeit that was masterseal and they're neons as opposed to led's , these scame switches are fairly new to me, my supplier got them in recently so i thought i'd try a few
 
I've just been called back to this same job because the switch stuck on again last night , I replaced it with another Scame switch and it done the same thing, so I then replaced it with a gewiss one I've had on the van for a while and it's fine now, switches off and on and doesn't do anything untoward. Has anyone else had this happen? I really am stumped as to what caused it on the Scame switches and not the other one
 
sounds like it's got to be the LED indicators causing the problem. why not get in touch with scame and explain the problem. they might have a solution.
 
Well that's the thing, I thought it was those causing it but its doing it without them connected, I've never had it happen before, it must just be the switch but why I don't know:-(
 
I had two Scame 2G sockets, both of which broke after less than a month of use. On top of that, each outlet had independent terminals meaning I had to link between the two! I haven't used again. I run with MK or Gewiss now.
 

Reply to Scame weatherproof switch sticking on in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I’m looking to install 3 meross smart switches for 3 lights: entrance switch: only 1 gang but 3 way switch bedroom switch: 2 gang (1 is 1...
Replies
9
Views
344
I usually always take a picture before disconnecting electrical wiring and this time I did not. I am trying to wire a 3way switch that controls...
Replies
0
Views
565
Hi All, thanks in advance for any guidance you can provide. I will of course turn off everyhing at the consumer unit before doing anything. I...
Replies
0
Views
444
I'm just replacing a 2 gang switch that controls the two ceiling lights in the living room with an updated one and I'm puzzled about the current...
Replies
3
Views
2K
Ok guys, first post so be gentle. I have a standard setup of two two way switches, one at the bottom of the stairs and one at the top so the light...
Replies
25
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock