Discuss Schedule of circuits - Lighting FCU on RFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
On a couple of recent EICRs I've run into FCUs on a RFC, then 1.5 or 1mm to several lighting points and would be interested how people would note this on the schedule?

On the most recent one there are 6 outside lanterns fed from an FCU on the socket circuit, with max R1+R2 outside of 4.5Ohm (Dodgy joints partly to blame I suspect, but didn't have time to further investigate).

Putting it as the highest reading on the main RFC circuit doesn't make it clear that there isn't a very poor connection on the sockets that should be investigated. It would also look as though the RCD is being used for fault protection on that circuit without further clarification.

Would you note the fused circuit as a separate circuit in the schedule list, noting 1362 as the OCPD (which means it's well under the 15.6 max Zs). If so, how do you make it clear which circuit it's fed from? I'm thinking of just listing it as "FCU Garden Lights fed from circuit x" - Seems overkill to consider it as another db with a second page of test results just for a fused spur.
 
R1+R2 outside would be including the impedance of the fuse itself wouldn't it?

Good point - yes In this case it would because I didn't isolate at the FCU and test just the load leg. I guess if I was treating it as a sub board that would be the correct way to do it - with Zdb at the FCU and its own page - but that seems a bit OTT for a single FCU?

If this had been a spur to an outside socket and I got a higher reading, then I'd just put it down and move on, but because the cabling changes I'm just not sure how to detail it so that it's clear what is going on.

The max Zs outside would be well within the 1667 limit since there is an RCD, if that was considered to be offering fault protection - but anyone glancing at the sheet in the future may not be clear on what's going on, so I just wonder how others would note it...

In reality, the 1362 is providing fault protection for that part of the circuit and the RCD is offering additional protection.
 
As I think about it the 13A fuse wouldn't really change it at all...sorry.
(What erroneously came to mind was I once carefully nulled a wander lead as 0.60 ohms, then measured some 10mm gas bonding at over 1 ohms. Nonsensical, was driving me nuts. Then I realised I'd accidentally picked up a probe from a different meter and it had a fuse in!)

To answer the question...
I'd probably loop test the end light, IR test the spur wiring, and just add additional notes that the outside lighting had appropriate basic and fault protection. In the same way I don't detail every fan, boiler and other accessory on a spur, as long as it appears to be safe and has appropriate protection I wouldn't lose sleep about it if it seems safe.

As you say, with different wiring with smaller csa it's equally misleading to record the Zs on the load side of the FCU as the highest measured Zs for the RFC.

However in this case I would probably add an FI regading the high Zs - quick and simplified maths suggests Zs of 4.5 ohms in 1mm T+E is about 120m of cable (assuming equal conductor sizes and Ze of 0 for quick mathematical convenience). I'd want to know Zs at the supply side of the spur as a starting point too.
So even though I completely agree additional RCD protection will save the day I'd want to mention something is up and it needs looking at.
 
The FCU should be counted as one point of the RFC.
The subsequent lights are a subsequent circuit protected by the 1362 but, not really worthy of a second schedule sheet.
A second line, with explanation, is OK.
A good case for explanation in the notes.

I had a bit of a problem a few years ago where a mate had little choice but to extend kitchen lights from a FCU and another spark failed it due to slightly high Zs (RFC). He asked for help. I explained it's not ideal but it is a sub circuit. Fused down, smaller cable.
 

Reply to Schedule of circuits - Lighting FCU on RFC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Situation is garden summerhouse fed by own 16A RCBO in consumer unit in garage over 4mm2 (overkill !) SWA . At summerhouse this goes to sockets...
Replies
13
Views
2K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock