Hello,

I am currently working on a project that previously utilises a charger for a battery system that is connected via single phase 240V AC mains. The existing charger has the 15A inlet running through a 1P 16A schneider MCB with the active line connected to the MCB (with earth and neutral bonded with BP's), which then outputs to the charger.

My question is, is it possible to replace the regular 1P MCB with a 16A RCBO and if so, how is this wired? Specfically how can it be wired from the 15A inlet to the RCBO and RCBO to charger? I haven't installed an RCBO before and am unfamiliar with incorporated the neutral and earth line wires that come with the schneider RCBO..
 
with a RCBO, basically, you take the circuit N out of the N bar and feed from RCBO N. L is from RCBO L. then the RCBO tails go N to the N bar where you took the circuit N out. and the functional E (if fitted) goes to the E bar, preferably in same terminal as the E of the relevant circuit .
 

Reply to Schneider RCBO to replace MCB in the Australia area at ElectriciansForums.net

Similar Threads

Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
Replies
33
Views
4K
Hi guys, I have recently encountered that my circuit breaker for the upstairs lights keeps tripping. I flick it back on and immediately it trips...
Replies
7
Views
901
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi, I want to add a change over switch so that a portable backup petrol generator can be used when grid power goes down. As it has in Victoria...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock