A central battery system with a non maintained mode of operation will generally have sensing circuitry to activate it upon loss of the general lighting. Maintained systems don't require this as fittings are illuminated at material times, maintained systems are often operating as "floating" whereby it is the batteries operating the fittings at all times so there is no change over period in the event of power loss.
 
Quite often the local circuit will power the coil in an emergency lighting relay unit, this opens the NC contacts and the emergency lights in that area are off. If the local circuit loses power the relay lets go and the emergency lights illuminate fed from the supply from the central battery system. the only ones I've done anything with all output 240v all the time from the mains to all the relay contacts, if the central battery unit loses power the inverter then supplies the 240V.

The other type of system I've worked with has the same arrangement but the local circuit feeds the relay coil, the rooms switched supply feeds the relays NO contacts, the battery supply feeds the NC contacts and the common connection is to the rooms light fittings, so the main lighting becomes emergency lighting if the power fails. I've only seen this setup in listed buildings where emergency bulkheads would not look good in the property.
 
If the OP is indeed testing a central battery or static inverter system then they should be testing at the unit, including battery tests with a battery tester, as well as checking any arrangements for non-maintained operation.
 
Deafening silence from the OP, so while we await his return, let me show you what a *proper* mains voltage central battery control unit looks like. It's in full working order although the 120-cell lead-acid was long gone by the time we rescued it. Not sure if I've put up pics of this before, if anyone is interested I can give you a guided tour of the equipment cabinet. BTW the bulb's name is Amy.

AMYSIDEOPENLIT.JPG

AMYBULBSIDELIT3.JPG
AMYVOLTMETERON.JPG
 
Lovely. Something magical about that blue glow from them eh.
 
Just replying to SWD's post above. Makes sense to me. I think :)
 
Its Polish for a "narked" or something along those lines. Polish people don't understand the English sense of humour lol.........

As my parents where Polish I have the double dilemma of both English and Polish people not finding my jokes or sense of humour funny :D:D:D:D
 

Reply to Selfridges Emergency battery test in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top