Hi!
I have a led strip (12V) with an external cable (2*1mm) glued on the wall and it's not fancy at all..
Inside the wall I have 3*1,5mm cable with 220V
Can I put both cables together inside the wall?

Thanks
 
Mixed voltages in the same containment are allowed providing all the different insulation ratings are higher than the highest voltage carried by any cable.
 
Sorry just seen that you are in greece.
I have no idea what is allowed over there so please disregard my earlier post.
 
Without knowing the Greek electrical regulations, the suggestion by @James that follows the UK regulations is good general advice.
ΟΚ
So, this is my 12V cable,
kalodio-reumatos-nymhy-h05vv-f-2g1 copy-800x800~2.jpg

And there are 3 pieces of that cable (220V) inside the wall,
kalodio-monopoliko-nya-h07v-u-pvc-4mm-mavro-normal.jpg
What do you think?

Thanks
 
So, this is my 12V cable,
It looks like normal 230V rated cable. Sometimes there are type and rating info embossed in to the cable every metre or so, but not always easy to find (especially on short lengths where it might be missing)
And there are 3 pieces of that cable (220V) inside the wall,
Looks like typical single conductor wire as used in the UK in trunking or conduit.

Simple based on the images it looks fine, but take care that any joints, connectors, or similar are also adequately rated to max voltage.
 
It looks like normal 230V rated cable. Sometimes there are type and rating info embossed in to the cable every metre or so, but not always easy to find (especially on short lengths where it might be missing)

Looks like typical single conductor wire as used in the UK in trunking or conduit.

Simple based on the images it looks fine, but take care that any joints, connectors, or similar are also adequately rated to max voltage.
Thank you!
My 220V cables have one connection with wire caps.
I'll tape that connection with 3M Vinyl Electrical Tape or similar for insulation reinforcement
 

Reply to Selv together with pelv in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
799
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
616
Since the deco needs doing to this property. My sister needs the TV putting on thr wall but wants the cables hiding. What will be the best way...
Replies
4
Views
350
Hi, plumber here so please be gentle (or take the p-ss ;) ), I am supposed to be installing a UV water steriliser for a customer. I have some...
Replies
16
Views
2K
Hello, my house was built in the 1950s and every time I look behind a wall plate the wiring isn’t how it’s shown in any DIY book I’ve read. I’m...
Replies
4
Views
912

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock