Discuss Sensible answers only !!!!!!!!!!! in the Electricians' Talk area at ElectriciansForums.net

G

Gethyn Turnbull

Hello fellow sparks,
right can anyone answer this . I have a generator which is running a bailing machine . The main isolator on this machine is rated at 680 amps quite a heavy load to operate this equipment (3phase ) what my customers want is this to be run of the mains because it costing a £1000 a week on diesel ! There is a small sub station which isn't being used about 80m away from the bailer. I've contacted western power and I've stated filling in the form and they asked me what power requirements I the customer require . Kva... Is this equation right for me to answer this

kila volts amps = amps x volts / 1000

therfore 680 x 400 (3phase) / 1000

272 kva ???????

is this correct .

Regards
 
you can't go by the isolator rating. it could be way over the actual load. you need to either look at the machine's rating plate, or clamp meter a phase and read you A/phase, then calculate the KVA from that.
 
what rating are the fuses/MCBs on the supply to the machine?
 
That's going to cost at least a years worth of Diesel for W.P.D to do their bit, plus the cost of electricity on top.

Is the baler permanently sited?
 
Your Kva equation is right for single phase equipment only, theres another slightly different equation for 3phase, cant remember exactly what it is but im sure if you google Kva 3phase equation you will find it
 
Whatch out for those Killa volt amps. Very nasty.

How can anyone give a sensible answer to such a question? You clearly haven’t a clue as to what you’re asking.
Either get some realistic figures or find someone that does know what they are on with.
 

Reply to Sensible answers only !!!!!!!!!!! in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K
Looking at a warehouse contract which requires 190M runs of canalis with 31 x 200w lights. Volt drop is 0.72V per Amp per 100M for 25A 3phase...
Replies
2
Views
957
Hello, this is my first post here. I have a little experience with most types of household wiring through a decade of DIY remodeling, and...
Replies
0
Views
789
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock