Dear Members,

Seeking your view to assess a risk for replacement one length of PVC/SWA/PVC Cable.

Back Ground:

A 90 KW Motor is connected to Star-Delta Starter in MCC at a distance of 200 meters, by 2 runs of 3-core70 mm2 PVC/SWA/PVC cables buried directly underground.

One length having an underground joint covered in concrete recently develops earth fault, one core shorted to ground.

Intend to replace only one length of 3-core faulty cable, laying on surface cable tray that carries other small power and control cables in stead of underground due to majority length of existing cable route already covered by concrete.

Concerns:

Will separate run cable on surface mounted cable creates eddy current since it is not bundled with the other length of cable?

The existing galvanized metal cable tray has metal cover of most of its length.

Thanks,

chlee-penang
 
In general, paralleled cables should be arranged to ensure uniform current sharing under all conditions including fault, and it might be difficult to achieve this with your different installation conditions for the two runs. Because of this it would probably be non-compliant with UK regulations other than as an exception. The only real cause for eddy currents under running conditions would be assymmetry in the cable core impedances; this would cause a nett longitudinal current along the tray which could couple into the control circuits as common-mode voltage.
 
In general, paralleled cables should be arranged to ensure uniform current sharing under all conditions including fault, and it might be difficult to achieve this with your different installation conditions for the two runs. Because of this it would probably be non-compliant with UK regulations other than as an exception. The only real cause for eddy currents under running conditions would be assymmetry in the cable core impedances; this would cause a nett longitudinal current along the tray which could couple into the control circuits as common-mode voltage.

Dear Lucien,

Thanks for your expertise advice, seeking your further clarification.


1. Disregarding the two run of cable installed in different route and method, even replacing both cables to be run in same cable tray, the assymmetry in the cable core impedances will still present on each length of cable when starter switches to Delta running condition inducing common mode voltage to other control cables right?

2. Am I right to say that, running one cable on cable tray present common mode voltage, it also creates heat on section of cable tray with cover?

Thanks,
 
Anyone out there could share your view?

Our colleagues feel that there is no harm to replace only one length of cable, on the argument that even replacing both cables, impedance of each run remains the same and the circuit is in series not parallel.
 

Reply to Separately Run PVC/SWA/PVC Cable for 75KW S/D Starter Motor Create Eddy Current? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
487
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
I need to augment the underground supply to remote workshops at my own house. I’m struggling to understand the practical implications of voltage...
Replies
11
Views
2K
We have recently purchased a home in TX built in the 1920s, and the wiring is an assortment of multiple wiring events. There aren't any local...
Replies
2
Views
2K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock