Discuss should i get rid of an european sandwich maker 16A 250V? in the Electrical Tools and Products area at ElectriciansForums.net

maxaue

DIY
Reaction score
1
Hello to everybody, i am a not expert person in matters of electric devices, infact i think i naively made a mistake in buying a device from spain and realizing here it was not fit for the Uk sockets. Its a sandwich maker 250v 16A that anytime i switch on triggers the circuit breaker . Now i am wondering if i have to throw it away or if someone could be skilled enough to modify the wire or suggest me an adaptor that might make it work with 13A
Thank you very much
 
It sounds faulty. Using a 16A product like that on a UK 13A socket will overload it, but you are looking at many minutes for fuses to go, etc, so what you typically see is it works but gradually damages the plug and socket through excess heat.

If it trips immediately that is either a very high fault current (over 3 times the breaker's rating), or it is leaking to earth and tripping the RCD.

Given the cost it is probably not worth bothering with, take a look in places like Argos, Currys, etc, for a UK replacement.
 
Are there shops in london where taking it to be fixed? I rarely see them or simply i dont know them. I paid it 90 pounds plus delivery costs, if i can pay less than 40 pounds i would try
 
Mines a much lower power two sandwich toaster made by Breville only 850 watt, how many sandwiches do you make at a time? sounds commercial at that power, rather than domestic.
 
Last edited:
The device should have a nameplate or sticker detailing power and voltage.
can you post a picture?
 
i simply reported the symbols and numbers on its the schuko jack, while the adaptor i normally use for schuko is 250v 13A max
If you are saying 16A because that's what is stamped on the schuko plug, that doesn't mean the sandwich maker will necessarily take that current! As James post above - what does the rating plate say the wattage and/or current is? That information will also be in the instructions if you have them.

As has been said, It's likely tripping the breaker because of a fault.

PS it doesn't seem likely to me that a toaster has a 4kW element!
 
Last edited:

Reply to should i get rid of an european sandwich maker 16A 250V? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

Hi folks, new member here. I am a DJ/electronic music producer with basically zero experience in advanced electronics. I recently bought the...
Replies
6
Views
2K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock