Discuss Shower Cable and insulation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
8
Hey all,
Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs shower. I ran a 10mm from the CU to a stud partition where the Isolator sits and then onto the shower. About 15-20m in total.
Ive gone back today and seen that the shower the plumber installed is a 9.8kw so ill change the RCBO from a 40 to a 45A which is no problem however.... it appears they have used 60mm or 100m mineral wool insulation in the stud which I didnt consider. ( I know I should have)
I have no idea how they have insulated the cable for this 2m run ie 102 or 103 as i wasnt there when they insulated and boarded but according to the regs book it is now either rated to 47A or 32A depending on wether they sandwiched the cable or just pushed it back against the plaster board.
Asking the homeowner to change the shower is very unappealing as he would be limited to 7kw and its already plumbed in.
Clearly I cant derate the RCBO to 32A etc and I cant change the cable either.

How would you guys proceed regarding the insulation ? Would you even change the RCBO over ? I cant imagine its likely to trip drawing 42.6A on a 40A RCBO
I really appreciate the guidance of you guys in here on this.
 
Hey all,
Ive been in and out of a huge house rewiring as the renovate it for a year of so. Every is thing done and dusted except the downstairs shower. I ran a 10mm from the CU to a stud partition where the Isolator sits and then onto the shower. About 15-20m in total.
Ive gone back today and seen that the shower the plumber installed is a 9.8kw so ill change the RCBO from a 40 to a 45A which is no problem however.... it appears they have used 60mm or 100m mineral wool insulation in the stud which I didnt consider. ( I know I should have)
I have no idea how they have insulated the cable for this 2m run ie 102 or 103 as i wasnt there when they insulated and boarded but according to the regs book it is now either rated to 47A or 32A depending on wether they sandwiched the cable or just pushed it back against the plaster board.
Asking the homeowner to change the shower is very unappealing as he would be limited to 7kw and its already plumbed in.
Clearly I cant derate the RCBO to 32A etc and I cant change the cable either.

How would you guys proceed regarding the insulation ? Would you even change the RCBO over ? I cant imagine its likely to trip drawing 42.6A on a 40A RCBO
I really appreciate the guidance of you guys in here on this.
It won't cause it to trip, but it still means that it's operating above the load it's designed to sustain and therefore also running hotter than intended. It isn't a compliant design.
 

Reply to Shower Cable and insulation in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
4
Views
164
I have a fuseboard change I need to do soon I’m putting in a FUSEBOX 7 or 10 way RCBO+ SPD My only concern is how I should run the pyro cables in...
Replies
16
Views
1K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Afternoon all. I’m doing a dorma / loft extension all circuits for that extension are new . I’m going to upgrade the consumer unit also to...
Replies
1
Views
960
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock