Need to dust off the old books, I think I was getting confused with the amp thing as I would be calculating say the 9.5kw of the shower where of course ohms law throws that out the window because the 9.5kw is only relevant to the expected supply voltage so less voltage less kw less amps. Have I got there
spot on .example. a 10kW shower rated at 240V.

P = V x I, so
I = P/V = 10000/240 = 41.667
from this you can determine the resistance

R = V/I = 240/41.667 = 5.76 ohms.

now as the resistance is constant ( not allowing for temperature variations, then apply 230V to the constant resistance

I = V/R = 230/5.76 = 39.93 A

from that, P = VI = 9.184 kW

so the actual current draw and hence the power, is reduced.

can't you telli'm bored and got nowt better to do. it's pi$$ing down, so car wheel theft is not an option for this Scouser today.:D:D:D:D:D.
 

Reply to Shower overheating no loose connection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Bit of a strange one ive been told by everyone ive called had a triton t70xr 8.5kw The water started running cold like the tco kicked in after a...
Replies
3
Views
1K
So abit of a random one. But yesterday my Neighbor asked me if I'd be able to take a quick look at their shower as it had stopped working. I said...
Replies
14
Views
2K
Hi guys, first time posting, please bare with me! I have an old test chart as shown in the pics that i would like to get running. Everything...
Replies
3
Views
869
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock