Got called to customer who has had a shower replaced 2 months ago by a plumber. Keeps blowing the fuse...

Turns out the replacement shower is rated at 10.5 kW.

Here is a picture of the consumer unit:

20210212_100901~3.jpg


The shower is actually fed from the 15 amp BS1361 fuse for the immersion heater, next to the lights. Along with the immersion heater!
The fuse carrier is now permanently welded closed.

The good news the circuit is wired in 10mm cable.

Bloody plumbers!

Needless to say I'll be returning next week to test the whole flat and replace the consumer unit...
 
In laws got a shower upgraded to 9.5kW, a couple of years back, and recently asked me to take a look a it as fuse was blowing periodically.

You guessed it - 32A fuse in a melted carrier and 6mm cable.

Told them to get a spark in as a matter of urgency and not to use that shower until then. It's going to be a new board for a number of reasons, so it seemed best that the news should come from someone with qualifications. Chances are they've ignored the advice and will carry on until they break the fuse carrier. Terminations are all good and show no signs of thermal damage, but that fuse must be getting seriously hot.

Apparently the spark who installed this shower mentioned that the set up "wasn't ideal".
 
I am very old fashioned and have always fitted gravity showers in my properties, do people go for electric showers because they are easier to fit, or is there some other reason?

Or on another tack, with the modern trend towards mains pressure hot water tanks, I would think shower installations will change in the near future.
 

Reply to Shower replaced by plumber blows fuse in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, Small flat, currently has a small'ish feed water tank, top of a cupboard, feed through a wall into under stairs cupboard. Hot water tank...
Replies
5
Views
466
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Run into this today at a house my nephew is moving into.... Original Dolphin 860 Shower (8600W) installed on 6mm Twin and Earth - maybe 15m...
Replies
4
Views
4K
In our house the main fuse is rated at 100A maximum. The individual circuits in the consumer unit, if all used simultanuously, add up to much...
Replies
38
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock