Discuss Single phase motor reverse rotation in the UK Electrical Forum area at ElectriciansForums.net

waigy

-
Reaction score
0
Brook Crompton Parkinson single phase PD90S (from the 70s) 240v 11A 2850rpm 50hz
I'm using it for polishing metal with a tapered spindle adapter and buffing wheels.

I've got 2 questions.

1. (This photo was taken with all the wiring in its original position.)
I've managed to reverse the motor rotation by swapping the two black wires that are behind the copper connector, but after a few quick trials it is constantly blowing fuses.
Can you confirm that I have changed the correct wires to reverse the rotation?

2. The capacitor starts the motor with a massive jolt which forces the buffing wheel so far onto the tapered spindle that I need large pliers to loosen the buffing wheel.
If I fitted a smaller capacitor would it start more gently or is it possible to remove the capacitor and start the motor by hand by rotating the buffing wheel?

The white arrows point to the three wires that go inside to the motor.
P1010335.jpg

[automerge]1582900380[/automerge]
UPDATE.
I just sorted the problem of blowing fuses.
I fitted new bearings to the motor a couple of days ago and noticed straight away that the motor was more stiff to turn and wouldn't turn freely if twisted by hand.
I thought that was just the bearings being a tight fit, but I slackened the 3 long bolts that hold the whole casing together by just a touch and it loosened the shaft a lot and it now can spin freely by giving it a quick twist.
It now spins for a long time after the motor is switched off which it didn't do before.
So I've tightened the 3 bolts just enough to keep the motor spinning freely.

But I still have the problem of the capacitor starting the motor with too much force.
I have a metal tapered spindle slid onto the splined end of the shaft which is a fairly tight fit.
That is then held in position by a 6mm screw to stop it rotating on the shaft.
The capacitor starts the motor so violently that the 6mm screw can't hold the tapered spindle on.

I have managed a work around just now of spinning the buffing wheel by hand as fast as I can, then switching the motor on while the wheel is already spinning.
[automerge]1582900603[/automerge]
And the motor is now spinning in the direction I want and working fine so my original question about what wires to swap seems to be answered too.
 
Last edited:
Are you sure because if that is the case it is not reversible. Many single phase motors state on the rating plate which wires to swap to reverse it.
 
It's working fine in the opposite direction

Did it jolt to start in the original direction?
Swopping the 2 wires you say you swopped won't have made any difference, they were both connected via the copper bar to Neutral and still are.
There are 3 marked with arrows, which 2 did you swop?

There ar 10 wires in total across 4 terminals
2 Capacitor
2 Capacitor
2 L+N
Leaves 4 out of the motor.

The bearings need knocking onto the motor shaft a bit more to stop the jamming.
 
But aren't you spinning it by hand to start it.
[automerge]1582905503[/automerge]
Did it jolt to start in the original direction?
Swopping the 2 wires you say you swopped won't have made any difference, they were both connected via the copper bar to Neutral and still are.
There are 3 marked with arrows, which 2 did you swop?

There ar 10 wires in total across 4 terminals
2 Capacitor
2 Capacitor
2 L+N
Leaves 4 out of the motor.

The bearings need knocking onto the motor shaft a bit more to stop the jamming.
I can only see nine wires leaving three from the motor.
Correction I can see ten now.
 
I missed the wire at the bottom which also goes into the motor so there are 4 wires going to the motor.
I have only swapped the two wires I mentioned before, the ones connected to the copper bar and that makes it run in the opposite direction.
It always starts with a jolt in both directions.
I'm only spinning it by hand to avoid the jolt over tightening the buffing wheel or making the spindle come loose.
 
I'm counting on the terminals

Top left 3
Bottom left 4
Top right 1
Bottom right 2
Yeah I can see it now.
[automerge]1582906178[/automerge]
You need to locate the ends of the start winding and swap them. One will be at the neutral terminal possibly marked 'S'.
 
Last edited:

Reply to Single phase motor reverse rotation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Friend of mines dryer machine has stopped working, 2 days out of warranty. I am trying to help theme out as money is tight for them however, I'm...
Replies
1
Views
666
Hi I have inherited a compressor with a single phase motor but its been stripped and I need to fathom out what's what.. I don't know if it even...
Replies
13
Views
633
Hi, First of all I must explain why my posting came to be on this site, I was looking on the internet for a forum that could help with a project...
Replies
8
Views
1K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock