If they are plug & socket they have to be RCD protected and with that many drives you are likely to have issues of accumulated leackage causing false trips if it is a single supply.So that’s all that is needed?
Because I was going to install 6 of these servo drives in an electrical
Cabinet.
So you advise just to keep it simple and leave it with fuses.
I was dreaming of a very pretty electrical layout within a electrical enclosure so you advise that it is best just to put some 6 way gang sockets and just plug em
In simple… hmmmm
Also if you have 6 drives each of 10A and any real possibility of them simultaneously running at rating then you need a 60A supply in total, that is going to require 2 * 32A feeds for the lot, even if they are each on 13A fuses at the end.
To avoid the plug & socket and thus RCD requirement you could hard-wire them in to FCUs instead, so say two 32A radial so 4mm cable (if clipped direct and not in hot zone or thermal insulation) each supplying 3 drives via 3 FCUs would be an option.
If they have to be removable thus plug & socket you would need to investigate the leakage, as you might have to put in 3 * 25A RCBO feeds or similar with each doing 2 * 13A socket, etc.