So that’s all that is needed?
Because I was going to install 6 of these servo drives in an electrical
Cabinet.

So you advise just to keep it simple and leave it with fuses.

I was dreaming of a very pretty electrical layout within a electrical enclosure so you advise that it is best just to put some 6 way gang sockets and just plug em
In simple… hmmmm
If they are plug & socket they have to be RCD protected and with that many drives you are likely to have issues of accumulated leackage causing false trips if it is a single supply.

Also if you have 6 drives each of 10A and any real possibility of them simultaneously running at rating then you need a 60A supply in total, that is going to require 2 * 32A feeds for the lot, even if they are each on 13A fuses at the end.

To avoid the plug & socket and thus RCD requirement you could hard-wire them in to FCUs instead, so say two 32A radial so 4mm cable (if clipped direct and not in hot zone or thermal insulation) each supplying 3 drives via 3 FCUs would be an option.

If they have to be removable thus plug & socket you would need to investigate the leakage, as you might have to put in 3 * 25A RCBO feeds or similar with each doing 2 * 13A socket, etc.
 
1 drive, as you said comes fitted with a plug, easy.

6 drives in an enclosure needs a proper design process and is out of the realms of a little diy advice.
 
Hard wire individual circuits back to DIN fuse carriers?
 
Hard wire individual circuits back to DIN fuse carriers?
Yes, that is an option to have a DIN box of them and then a 63A feed from the main panel. Finding a suitable bus-bar might be harder if so many on single big supply.

Might be just as easy to have a local CU of 6 * 16A MCBs!
 
im stucknow,

so 6 mcb's with magnetic contactoras suggested in manual drawing for 3 phase althought imusing singephase 240v (theres no drawing for that)

or 6 din fuse rail way.

and using 6 bus bars (3+3); 2 for live 2 for neutral and 2 for earth. and using two seperate 40A feeds from main power box.

sounds good yeah?
 

Reply to sizing up mcb and a contactor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello I have two new appliances Electric oven rated at 3.95 KW Induction hob rated at 7.2 KW total of 11.15 KW Currently it is on its own...
Replies
17
Views
4K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Background I live in Indonesia, the voltage for residential buildings ranges from 220 V to 230 V, I need help with the installation of the...
Replies
0
Views
3K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock