Discuss Small central UPS for converting circuit to emergency lighting in the Lighting Forum area at ElectriciansForums.net

Martin

-
Reaction score
2
I am looking for a product to convert an existing lighting circuit in a communal stairwell to be emergency battery backed up. There are 6x 7W LED mains fittings, so say a max 50W load. I could just add emergency lighting fittings, but wiring and access is difficult.

It also needs to have a switched line input, so existing switches can still be used to turn lights on/off. All switch lines come back to central junction, before going to light fittings. I am struggling to find a suitable unit.
 
So all you are trying to do it run the lights when the power goes off?

Fit a suitably sized UPS at the DB /CU to give the maximum time required.
From lighting MCB (plus N plus E) into UPS.
Connect outgoing of UPS to L, N, E of lighting circuit.
Existing switches remain.

Probably doesn't comply with E.M lights standards.
 
This is going to be essentially a central battery system. The cabling would need to have some kind of fire resistance and possible separation from other circuits. These lights are also switched meaning they may not function in the event of a power failure if switched off.
 
The easiest thing would probably be to fit self contained maintained fittings with microwave sensors and convert the s/l to permanent live with key switch for testing.

Adding an invertor/central battery will require all cables to be fireproof, so it will probably need to be completely rewired.
[automerge]1575295412[/automerge]
Also what happens when a fire burn though the central battery back?

That's a bit of a daft question, the answer should be ridiculously obvious.

This is why there are rules about the type and location of central batteries for emergency lighting.
 
Thanks for the replies, but no product suggestions so far.

Cable is MI, so is fireproof.

Essentially what I'm looking for is a very small central battery system, but these all seem to be designed to power whole buildings.

I can't find anything between this below link (8W), and a large central battery system.

I can't just use a standard UPS as it doesn't have a switched live input for functional switching of the lights. Also I'm sure wouldn't comply with EL standards anyway.
 
Is there a reason you cannot do what dave sparks has suggested previously?
I may need to go this route, but finding suitable looking fittings isn't easy. The client would prefer to keep the existing fittings and doesn't want a bunch of EM bulkheads.

Also since the switches are wired separately from the light fittings, it seemed the easiest option to just add one battery box with inverter.
 

Reply to Small central UPS for converting circuit to emergency lighting in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
879
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
657
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
646

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock