Discuss Small in size switch fused isolator in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Reaction score
158
On a rewire I am quoting for a flat- the old c/u is in a tiny cupboard in communal hallway
planning on moving new c/u inside flat (prob 1m to the right and 1.5m upwards)-this will be inside flat front door

was hoping to find a small in size 80a/100a switch fused isolator (non combustible) to be on the safe side if the tails from the old c/u position to new position may be close to 3m mark.

found this one which is d: 109mm h:303mm w 179mm
then mmt4 trunking between the two with 25mm tails +16mm earth

literally so cramped in this low level cupboard!!!!

http://www.NoLinkingToThis/p/wylex-80a-domestic-switch-fuse-unit/3359j
 
Last edited:
The meter tails should be as short as possible. Different metering companies have different policies but the length should always be less than 3 metres of cable from the cut-out through the metering equipment to the consumer unit. A example may be 1m of cable from the cut-out to the meter, then 1.5m from the meter to the consumer unit. The meter tail cable size must be consistent. BS7671 Reg. 434.2.1 gives some guidance. If the consumer unit is required to be further away, then a switch-fuse unit should be installed close to the meter and a sub-main compliant with BS7671.

The above is taken from the association of meter operators......for some reason I cant post a link but if you type association of meter operators in to google and click on their site, click stake holder info and then length of meter tails.
 

Reply to Small in size switch fused isolator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
0
Views
1K
Deleted member 155212
D
Hi all, I am looking to replace an existing CU (ground floor) and put it in a new position (first floor). The existing CU is on the inside of a...
Replies
8
Views
3K
Hi all, First post here, hope I'm compliant with the rules! I did do a quick search before asking this, but I couldn't quite come up with the...
Replies
3
Views
3K
Apologies if this is a regular question. I've been asked to quote for an EICR for a small block of flats, converted from a house. 3 x houses...
Replies
3
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock