derekmay

DIY
Reaction score
1
Trying to install a smart thermostat,
I have 4 wires red, yellow, blue and earth,
And this smart meter wiring diagram baffles me.
1st photo old thermostat,
 

Attachments

  • IMG20221127172544.jpg
    293.2 KB · Views: 20
  • IMG20221127172558.jpg
    232 KB · Views: 19
  • IMG20221127172614.jpg
    377.5 KB · Views: 20
À = 4
N = 3
C = 2

Printing on the back of the new 'stat indicates a second, volt free, switch connected to 5 and 6, but the paperwork shows a NTC resistor = temperature sensor connected to those terminals.
Your diagram for the old 'stat show B as neutral. This is not correct. B is the live end of the backset resistor.
If this is being fitted into a flush metal box, then the earth should be connected to that.
 
À = 4
N = 3
C = 2

Printing on the back of the new 'stat indicates a second, volt free, switch connected to 5 and 6, but the paperwork shows a NTC resistor = temperature sensor connected to those terminals.
Your diagram for the old 'stat show B as neutral. This is not correct. B is the live end of the backset resistor.
If this is being fitted into a flush metal box, then the earth should be connected to that.
So 2 is blue 3 is red, and 4 is the yellow wire
 
Can't answer that. I've no way of knowing what colour was attached where on the old 'stat. Pics before you disconnect are always good.
 
Can't answer that. I've no way of knowing what colour what attached where on the old 'stat. Pics before you disconnect are always good.
On the photo, a is yellow, b is brown, only 2 wires was connected.
 

Attachments

  • IMG20221127172544.jpg
    293.2 KB · Views: 1
On the photo, a is yellow, b is brown (red), only 2 wires was connected.

This is an unusual way for a thermostat to be connected. It's connected to break the circuit as the temperature rises - most are connected to close the circuit with temperature rise.
Also, conventionally red would be connected to A and yellow to B, although with just two wires connected it wouldn't make any difference to the operation of the circuit.
What is this 'stat connected to. You may have to examine the source end of the wire to see what's what. The blue may be neutral, but may not be connected at all.
 

This is an unusual way for a thermostat to be connected. It's connected to break the circuit as the temperature rises - most are connected to close the circuit with temperature rise.
Also, conventionally red would be connected to A and yellow to B, although with just two wires connected it wouldn't make any difference to the operation of the circuit.
What is this 'stat connected to. You may have to examine the source end of the wire to see what's what. The blue may be neutral, but may not be connected at all.
A Worcester green Star 4700 combi boiler
 
Any external programmer and/or wiring centre? Worcester 4700 manual doesn't show connections to a 'stat.
Red, yellow and blue wire indicates that the wiring is much older than the boiler.
 

Reply to Smart thermostat wires in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I installed a transformer for 5 smart thermostats, 1 of the thermostats trips the transformer fuse button right when I turn on the power. There is...
Replies
3
Views
629
Hi, i’ve been trying to buy a smart switch 1 gang 1 way but i opened my conventional wall switch and i only have 1 red wire(Live Old UK) 1 black...
Replies
3
Views
593
Hi everyone just looking for some advice before buying stuff not planning on carrying out this work myself will get someone who knows what their...
Replies
2
Views
405
I currently have a Myson thermostat that is no longer working. I have a Meross thermostat to replace it. I have attached photos of the current...
Replies
1
Views
1K
Hi All I have been asked to supply a minor works certificate on a smart thermostat upgrade. Would I just test the dedicated circuit from the CU...
Replies
3
Views
314

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock