Discuss smoke alarms vunerable to ir test? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

C

claire_r

hey all!!

would a smoke alarm circuit be vunerable or give out false readings on the live insulation resistance test? or is it worth me just connecting the lives and testing to earth? well and the interconnecter.

cheers all :)
 
When you IR test a smoke circuit you should disconnect the actual smoke detectors, then the circuit can be tested as normal and readings should be as normal, you should now that electronic equipment is vunerable when doing these tests and where possible should always be removed, if for some reason you cannot disconnect them all you can use 250v on your tester instead of 500v, but only in these circumstances.
 
Hi clare r, as KFORDHUNTER mentions you should remove the alarms where possible, it does'nt take long and then you know you are getting true results for the circuit.
 

Reply to smoke alarms vunerable to ir test? in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

I currently have a home with 7 interconnected, hard-wired smoke detectors. I have a hard-wired heat alarm in the garage that I need to have...
Replies
4
Views
2K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
639
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
673
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
355
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
696

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock