Hi Gavin,

I'm sorry. What I was trying to say is that there is no Cat5 cabling. The modem/router is connected directly to the master socket and the PC is connected to the modem/router by a short length of Cat5 cable at desktop level.
There is no additional cable involved in the installation of the iBoost.
What about the incoming broadband cable to the router?

it could be that the router is sensitive to the voltage flicker from the iboost, but usually they're powered via little transformers which should stop that being the case.
 
The past few days have been poor for Solar. Today much better. I therefore disconnected the immersion from the Solar iBoost and replaced it with a kettle.
The broadband problem still existed, but at least I had eliminated the heater element and thermostat.
Connected my laptop to the test socket inside the Master Socket.
Long story short - replaced the microfilter everything OK.

Solar iBoost now heating the water and I have a working broadband connection. All down to a microfilter.

Thanks for all your help and suggestions. Much appreciated.
 
The past few days have been poor for Solar. Today much better. I therefore disconnected the immersion from the Solar iBoost and replaced it with a kettle.
The broadband problem still existed, but at least I had eliminated the heater element and thermostat.
Connected my laptop to the test socket inside the Master Socket.
Long story short - replaced the microfilter everything OK.

Solar iBoost now heating the water and I have a working broadband connection. All down to a microfilter.

Thanks for all your help and suggestions. Much appreciated.
That's not the first time I've heard of a micro filter causing an issue but to be honest it's not something that would have occurred to me to suggest in your circumstances. Small innocuous devices that can cause perplexing problems!

I don't think you need one on the router (unless you have a phone plugged into the same socket) - you just need them for the phones.

good to hear the problem's solved.
 
Strictly you do need need one on the router, but as most routers nowadays come with RJ11 connectors then the adsl output of a microfilter provides the physical conversion from a bt socket. Not only does the microfilter prevent adsl interference being heard on the telephone line, but it also prevents interference picked up on the internal telephone wiring and interference generated by internal telephone equipment passing back to the router input. It was the first thing I suggested earlier because I have seen faulty filters cause the broadband to fail for a few seconds when a phone is taken off hook. The wiki article on dsl filter gives more for those interested and some links. Not all filters are created equal!
 
Yes, I did fix it. Please have a look at post number 12. Some time ago. Along with my solar panels turns out to be the best investment I have ever made. Hot water most days throughout the winter months. Definitely a happy chappy.
 
It was the first thing I suggested earlier because I have seen faulty filters cause the broadband to fail for a few seconds when a phone is taken off hook. The wiki article on dsl filter gives more for those interested and some links. Not all filters are created equal!

On a completely different note (and hijacking this thread :) ) we used to have that problem, however no seperate micro filters any where as BT had fitted one of their super duper master sockets with seperate outlets for broadband and phone and we had no extensions plugged in anywhere else. (I have two lines here, and the broadband is on the secondary line)

Upgraded to ftc recently and as part of that process of installing their modem they also fitted a new super duper master socket, when asking the engineer why, he couldn't explain - it was just what they did, - yet he didn't know if there was any difference whatsoever, anyway wether it's the mew master socket or the ftc process, the broadband doesn't drop any more :)
 

Reply to Solar iBoost Problem in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

4
Can someone tell me what the resistance should be for a Solar iboost Clamp? My clamp is regestering zero ohms and I want to confirm this is the...
Replies
0
Views
871
4Dave C
4
Hey guys, hoping someone can help with my problem.! A client of mine asked me to rig-up a little solar system to power a diaphragm air pump...
Replies
2
Views
1K
Hi, Similar'ish question to my other thread but little more info now so a different approach but sorry if duplication. UK, single phase. Just had...
Replies
0
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
HI Folks. This is my first post so apologies if it's in the wrong location. I recently installed a 3kw Solar system with an iboost diverter...
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock