45
Hi Guys,

I have quickly checked the forum and the net in general, I need a bit of advice regarding some solid core Aluminium twin and cpc.

I am adding a couple of sockets to a circuit and upgrading the board but the place is wired in solid core Aluminium. See pic.

I've seen somewhere that MK did specific accessories for this and of course they are no longer available so I was thinking that I will do all terminations into Wagos and then copper into the accessories, does that seem like a reasonable course of action?
What about in the new board? A separate enclosed for wago joints then onto the board?

Insulation resistance readings are okay so far.
Property is a top floor maisonette built and wired in the 60s/70s

I obviously be undertaking more testing of each circuit for the board change. Although i am not touching the lights I might recommend that I take them down, fit a joint above each one and bring copper t and e or flex into the fitting to cover for future DIY light changes etc, does that seem like a good idea?

It must have been at the turn of a price rise as the properties below this one (which i have worked on) are wired in MICC, which i was expecting to find in here.
 

Attachments

  • 1623663002191639910224236100756.jpg
    527.8 KB · Views: 27
In one way I like the Wago approach as it reduces a lot of the stress on the Au cores, also gives you a second chance when a few snap, and they will.

You are doubling the number of connections though, an issue?
 
In one way I like the Wago approach as it reduces a lot of the stress on the Au cores, also gives you a second chance when a few snap, and they will.

You are doubling the number of connections though, an issue?
Yeah adding more connections is not great but the lesser of 2 evils in this case.

The cores are quite firm but as soon as something is screwed in they could just snap. The old socket i removed they were twisted together so quite solid
 
Wago have guidance for connecting to aluminium wire, in particular they have a paste to exclude air/moisture to stop galvanic corrosion and help maintain a low resistance connection:

It is pretty rare to see this in the UK, but some folks to stock it:
 
Wago have guidance for connecting to aluminium wire, in particular they have a paste to exclude air/moisture to stop galvanic corrosion and help maintain a low resistance connection:

It is pretty rare to see this in the UK, but some folks to stock it:
Thanks for that. I will get some
 

Reply to Solid core Aluminium t+e in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've always disliked needing to wrangle three 2.5mm T&Es into one 13A socket. The three solid cores rarely sit cleanly, and there's always the...
Replies
45
Views
5K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi, this is a repost of the initial in diy as the only potential diy aspect is the prep ahead of a qualified person attending, this is hopefully...
Replies
2
Views
1K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
732
I never did like transformer theory in my degree course and that was 40 years ago. I'm a boat builder now and we tend to have big battery banks...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock