Thanks! Expensive is probably the word... though I'm having a hard time getting a price for a conductor area (did I get that right?) of 35 sqmm.

Yes, but it as @Rockingit points out in post #4 my figures are based on an anticipated maximum load of 13A. You should definitely take a look at his posts because if your can be fairly precise with your design currents and they are much smaller, the cable can be significantly smaller.
 
35mm² 3 core swa £13.50/m from
 
35mm² 3 core swa £13.50/m from
35mm the armoured would be fine for CPC so only need 2 core. That should reduce the cost of a 600m run by at least a pint.
 
In fact, thinking about it some more, if it’s going in a duct anyway then I’d be doing the maths for concentric service cable and a TT…

And thinking even more outside the box, for that ££££’s of cable two small LV-MV MV-LV transformers might even be cost effective with a much reduced conductor size cable. Outside the scope of BS7671 but doesn’t make it a bad engineering solution.
 
There was a similar post a few months ago that might be of interest, which also happened to be about 600m:

 
The 13A sockets are what puts the cost up. What are they for?
Thanks - security camera, recharge points for a robot mower, plug for laptop and a wifi point at most. I get the feeling I'm out of my depth on this one and not even asking the right questions. Sounds like I should dig the trench and leave everything electrical to a pro!
 

Reply to Specification of cable to carry power over about 600 metres in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
Hello all of you lovely electric-minded folks, I've read a few threads in the forums but none have explained what I'm looking to find out -...
Replies
9
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi all. I’ve joined the site to ask for a quick bit of advice. Please note, I’m not an electrician, I will be hiring one to complete the bulk of...
Replies
17
Views
2K
Ok Hello all and thanks for having me. I need some advice and joined this forum hoping to be pointed in the right direction. First off I am not...
Replies
31
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock