Search the forum,

Discuss Stables with horses supply, power & lighting etc.. in the UK Electrical Forum area at ElectriciansForums.net

Soulsurfer

-
Arms
Reaction score
143
Hi all, I have never had to look into a job like this before but I have had an enquiry from a customer who is having a supply brought from the road to edge of his fields / property by the dno and he has to supply cabinet etc.. at a great cost for the mains !

I have to look at a run of around 45 mtrs of s.w.a in a trench to stables, into a small consumer unit at one end of stables where horses will not be but just a storage area. Couple of sockets there adjacent to board, and all light switches there too out the way. They want lighting above the two stables where horses are resident and also floods front and rear outside plus a small sub out to another shed / tack room across the yard around 24 mtrs away. I am thinking a lot of armoured plus maybe a bit of conduit in stables to lights high level etc.. and rcbo cover but would 30mA be alright with livestock ?

Also if board was TT'd with a rod outside away from stables by around 3 mtrs or more is that likely something you would go for ? Only issue I can see is that all around are other fenced fields that have electric fencing so is that likely an issue with the rod and fence earthing rods etc.. ?? never done something like this before.

Also what protection / isolation device at start of mains to the main board?
A time delayed RCD S type at 100mA or similar as thinking just a switch fuse wont be good enough.

Thanks for any experienced thoughts.
 
The switches and socket outlets etc.. would all be in a separate area closed off from horses. You wouldn't believe the state of it at the moment ! Got some pics, flexes hanging next to horses faces all run from a petrol genny. If it's as horrendously difficult as it seems, I may just forget the job to be honest.
 
upload_2017-12-7_22-45-45.png
this might happen if don't get it wright.
 
Hi - SS, a few late night thoughts ... I suggest a 100mA S and fuse at the cutout end and a 30mA one up front in the remote board. The rod is important, perhaps use stacked 15mm by 1200mm. I have used two sets indendantly wired as part of reliability etc. Cabling up high, gal conduit. Get them to agree to regular inspection checks cause it will get knocked about.
 
Hi - SS, a few late night thoughts ... I suggest a 100mA S and fuse at the cutout end and a 30mA one up front in the remote board. The rod is important, perhaps use stacked 15mm by 1200mm. I have used two sets indendantly wired as part of reliability etc. Cabling up high, gal conduit. Get them to agree to regular inspection checks cause it will get knocked about.
Thanks chaps, I'm thinking it's beyond me, don't want any horror stories on me. Never as I said done anything like this and it's a bit of a learning curve that I wouldn't want to go wrong.
 
Thanks chaps, I'm thinking it's beyond me, don't want any horror stories on me. Never as I said done anything like this and it's a bit of a learning curve that I wouldn't want to go wrong
did one many moons a go
the dumb a** owners tried to put normal switches with the horses in the stable had to put the switches out side .
 
Hi - SS, a few late night thoughts ... I suggest a 100mA S and fuse at the cutout end and a 30mA one up front in the remote board. The rod is important, perhaps use stacked 15mm by 1200mm. I have used two sets indendantly wired as part of reliability etc. Cabling up high, gal conduit. Get them to agree to regular inspection checks cause it will get knocked about.

Dont like this set up. Id prefer switchfuse at DNO & isolate cpc @ stables db, youre importing an earth over 45M bound to cause some PD between true earth and imported earth.
Earth rod at rear of stables with 30mA rcd main switch would be a better set up imo
 
Dont like this set up. Id prefer switchfuse at DNO & isolate cpc @ stables db, youre importing an earth over 45M bound to cause some PD between true earth and imported earth.
Earth rod at rear of stables with 30mA rcd main switch would be a better set up imo

How far to put rod in away from stables though is my concern 3 mtrs plus and there are electric fenced areas, would they cause an issue as could probably run direct to rear of stables themselves and rod a good 10 mtrs plus away from any elec fence equipment too.
 
Hi bud,there are 20 questions more really,but,i wouldn't think of going all protective on the size/type of your RCD,standard rules apply.

I would put the effort on separation rather than ADS:)

Place all cabling in steel conduit or similar,do not have accessories,such as switches,ANYWHERE horses can be/reach,whether metal or not. A decent 14HH can bite the front clean off a single metalclad...seen it.

There are specs for animals,especially horses,regarding proximity to TT rod positions - just read up,and pick your spot.

10mA for 5mS would not mean neddy would make the show.

I feel your pain,as after dealing with the DNO,intractable as they can be,your customers will now want to spend any money they have left,on saddles,bits and hoof-oil ;)
 
Hi bud,there are 20 questions more really,but,i wouldn't think of going all protective on the size/type of your RCD,standard rules apply.

I would put the effort on separation rather than ADS:)

Place all cabling in steel conduit or similar,do not have accessories,such as switches,ANYWHERE horses can be/reach,whether metal or not. A decent 14HH can bite the front clean off a single metalclad...seen it.

There are specs for animals,especially horses,regarding proximity to TT rod positions - just read up,and pick your spot.

10mA for 5mS would not mean neddy would make the show.

I feel your pain,as after dealing with the DNO,intractable as they can be,your customers will now want to spend any money they have left,on saddles,bits and hoof-oil ;)
The dno are charging a packet for a small run to be honest ! Seems a real wasps nest this livestock carry on :(
 
Dont like this set up. Id prefer switchfuse at DNO & isolate cpc @ stables db, youre importing an earth over 45M bound to cause some PD between true earth and imported earth.
Earth rod at rear of stables with 30mA rcd main switch would be a better set up imo
Hi - with the exception you've deleted the upfront s RCD I've suggested, this is exactly what I had intended. Fully agree with you on earthing.
 

Reply to Stables with horses supply, power & lighting etc.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
So far I have never had to deal with a new supply but a possible site we are looking at will need some major changes and so I wondered if folks...
Replies
2
Views
750
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
733
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
43
Views
1K
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
915

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock