Hello Everyone.

I had to change a socket in a landlord property (enough said)

Did a check on the RCD and found that it was not working.

Even though the flat only has an old 4way wylex the land lord will not go for a new board.

so my question is what tests would I need to carry out for this job if I just replace the RCD.

I.E would this come under minor works?

Thanks
 
so my question is what tests would I need to carry out for this job if I just replace the RCD.

I.E would this come under minor works?

There are a standard set of tests that you'll need to do (see GN3) to satisfy BS7671 and Building regs.

A MWC will most likely need to be issued after the work has been completed.
 
it's a like for like repair, so not notifiable, but basic testing ( Zs, IR, RCD ) and a MWC. IMO.
 

Reply to Stand Alone RCD in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
889
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
Morning guys, I would like some advice, currently at my workplace, I am replacing a DB and existing wiring in a warehouse. One of the ways feeds...
Replies
4
Views
1K
Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock