Fair enough it's still not the starter

Just an example.
One panel I installed over 30 years ago controlling 4 x 15kw motors via s/d starters. In all those years the motors have all been changed just once with the odd bearing change, whilst I would say that at least 25 contactors have needed changing with contact damage due to load.
 
It's switching over and it will run for a while sometimes a few hours and then trip. It's running a vac pump. Just need to know how to test winding from the panel as the motor box is not easily accessible.
 
Are you talking IR or resistance testing
It's switching over and it will run for a while sometimes a few hours and then trip. It's running a vac pump. Just need to know how to test winding from the panel as the motor box is not easily accessible.
Are you talking IR or winding resistance testing
 
It could be a multitude of things, does the motor sound ok? rumbling or knocking noises could indicate bearings/ alignment problems, check the supply voltage at the panel (line to line and line to earth) then from there visually check for bad/burning connections ( does the panel smell of burning when first opened up?) then carry out all the dead testing checking contact resistance on all poles of the contactors not forgetting to check the resistance of the overloads themselves. Check that the resistance of the motor windings from the panel are balanced if not check at the motor terminals.
 
I've just seen that it's a vac pump, when these start to fail they can become very noisey (sticking or broken blades) and at the same time take longer to reach the preset vacuum (this can checked by asking the operator if they have noticed any changes).
 
I'm going for mechanical fault (or lack of maintenance) on the vacuum pump. Oil and filter candles need changing. Just a complete guess but as I can't see it, hear it, or test it I'm just having fun guessing.
 
Check at the main contactor and the delta contactor not forgetting the o/l unit. Identify the windings U1 start and finish U2, V1 & V2 and finally W1 & W2, these should have the same value, don't be surprised at the very low impedance readings. Also check for leakage to earth from U, V and W. Don't forget to check the input voltage.
If all above are present and correct including what was said in #24, then it's almost certain a mechanical problem.
 
Last edited:

Reply to Star delta testing help needed in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Good day to you. I need electrical drawings urgently and hopefully there is someone that can assist me. They are all for electrical trade test...
Replies
6
Views
798
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock