I've been testing a static caravan installation. At the plastic meter box outside the 'van (which contains an RCD, 16A MCB, meter and 16A socket for the caravan) I get a Ze of 20 ohms and 13.5A PFC. The earth is through the incoming looped SWA of 2 x 2c 16sq.mm cables (crude TNS from the point of view of this caravan but probably TT for the site). The RCD trip times are all fine so all is well.

If I put the earth lead onto the galvanised angle iron which supports the plastic box instead, I get a Ze of 1.16 ohms, 199A PFC!
I'd be more comfortable if the caravan had its own earth rod but I'm not responsible for the system, I'm only here to test the caravan and that is all fine. I'm tempted to bond the angle iron anyway.

If it was up to me every caravan on the site would have its own earth rod.

What does anyone else reckon?
 
Why bond something outside? It is not possible to create a zone of equal potential
 
I'm only here to look at the caravan which has the earth imported through the SWA. Yes ideally I would interrogate the site owner and test at the origin. From driving round the site I can see a few (2 or 3 out of a hundred or so) caravans which have what look like 5/8" earth rods beside their meter boxes, the rest just have the looped 2x swa's. So I assume the site is TT but it's really not my remit as I'm only looking at one caravan at the moment.

.
 
I assume this is the same thread as this one. This thread closed please keep the same topic to one thread.
 
Status
Not open for further replies.

Reply to Static caravan Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
875
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi, I've got to a point where I need to complete the EIC for the caravan I've been working on. This isn't a static caravan, so will be going from...
Replies
2
Views
1K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
969
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock