If you think the bill is wildly inaccurate from the evidence of consumption you can see then install a data logger or a temporary CT meter to check its accuracy.

If the metering turns out to be accurate then draw up a plan to make some easy savings such as converting halogen/filament lighting to LED, install timers on hot water cylinders and reduce water temperature, clean all the refrigeration condensors and check fridge door gaskets etc etc.
 
...I have calculated his total load from fridges etc info plates lights by counting and added about another 30A on top , and it comes to 119A total . Now this is spread over a 415V 3 phase supply , which i have clamp metered up and monitered the indivdual cores which average out Brown/red- 23A , black/yellow- 19A & Grey/blue - 42A , oh and the neutral comes back with 38A on it.This obviuosly is nowhere near 269KWH , and was thinking this rouge N current must be from a dodgy connection on supply side ? It is also obviously a potential overheating risk i would have thought ?

So, your average measured currents give about 20kW at 240V. Multiply by 24h, gives 480kWh per day. So I doubt that the supplier's meter is over reading.

I agree with Lucien, there's no problem with the neutral current, given the unbalanced load.
 

Reply to STRANGE NEUTRAL CURRENT !!!! in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
542
Greetings, I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not...
Replies
4
Views
900
Hi I've been planning to fit an outdoor junction box at the front of my house to hide a large brickwork hole and properly house the wiring...
Replies
9
Views
924
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
346

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock