Discuss Strange voltage on earth wire in the Lighting Forum area at ElectriciansForums.net

Reaction score
2
Hi, I've got a light with a ceiling rose in the kitchen. While rectifying some faults in the house I came across to the light and measure Neutral to live: 240 volts (which is fine ofc) however when measuring earth to live I'm getting 150 volts. I have checked for any touched wires with my Fluke t6 but I could not find any. I am also getting voltage on the screws of the light switch according to my dodgy neon test lamp. Cheers
 
There is likely to be a high resistance connection to earth somewhere.
Yeah your right. ATM i think its fine atm because touching the screw of the switch does not give a shock but it lights the neon lamp sometimes very bright and sometimes not that bright. The light switch are old ones that get their feed direct from the swich rather than from the pendant
 
I think you misunderstood, a high resistance to earth on any cpc is a dangerous fault.
 
Wouldnt it just not display anything on the multimeter

Unconnected wires that lie alongside energised ones will show a voltage to earth because of capacitive and resistive leakage between them. Even with wiring in perfect condition, a small amount of current transfers capacitively through the insulation from line to CPC (earth conductor) which would normally flow harmlessly to earth. When the CPC is disconnected from earth, the leakage manifests as a raised voltage at all points downstream of the break. The leakage in itself might be harmless as the available current is usually too low to cause a shock, but it is a tell tale that the earthing is faulty and will not provide the necessary safety when required.
 
Unconnected wires that lie alongside energised ones will show a voltage to earth because of capacitive and resistive leakage between them.
in addition to the above you may also have some current flowing in the earth resulting from the "intentional leakage" built in to many modern day appliances .But as alluded to by the previous posters ,regardless of the type or leakage source the solution remains the same....repair the defects in the house,s earthing system
 
Unconnected wires that lie alongside energised ones will show a voltage to earth because of capacitive and resistive leakage between them. Even with wiring in perfect condition, a small amount of current transfers capacitively through the insulation from line to CPC (earth conductor) which would normally flow harmlessly to earth. When the CPC is disconnected from earth, the leakage manifests as a raised voltage at all points downstream of the break. The leakage in itself might be harmless as the available current is usually too low to cause a shock, but it is a tell tale that the earthing is faulty and will not provide the necessary safety when required.
Thanks bud! Cleared my doubts.
 
Unconnected wires that lie alongside energised ones will show a voltage to earth because of capacitive and resistive leakage between them. Even with wiring in perfect condition, a small amount of current transfers capacitively through the insulation from line to CPC (earth conductor) which would normally flow harmlessly to earth. When the CPC is disconnected from earth, the leakage manifests as a raised voltage at all points downstream of the break. The leakage in itself might be harmless as the available current is usually too low to cause a shock, but it is a tell tale that the earthing is faulty and will not provide the necessary safety when required.
You're technically right Lucien. However if the earth wire is disconnected in his case would it just NOT read from earth to live?. I have seen this in some properties. When he said 150 volts from earth to live this could indicate that the rest 70 volts are missing. Where are they missing? This looks pretty dangerous. :)
 
You're technically right Lucien. However if the earth wire is disconnected in his case would it just NOT read from earth to live?. I have seen this in some properties. When he said 150 volts from earth to live this could indicate that the rest 70 volts are missing. Where are they missing? This looks pretty dangerous. :)
If you think about the equivalent circuit of the situation (disconnected earth) you would have resistance, capacitance, inductance etc. between the various conductors as Lucien explains, which can ultimately form a potential divider together with the impedance of the measuring instrument, so you get a reading dependent on the ratio of those circuit elements. No volts are missing. It's just physics!
 
If you think about the equivalent circuit of the situation (disconnected earth) you would have resistance, capacitance, inductance etc. between the various conductors as Lucien explains, which can ultimately form a potential divider together with the impedance of the measuring instrument, so you get a reading dependent on the ratio of those circuit elements. No volts are missing. It's just phys

If you think about the equivalent circuit of the situation (disconnected earth) you would have resistance, capacitance, inductance etc. between the various conductors as Lucien explains, which can ultimately form a potential divider together with the impedance of the measuring instrument, so you get a reading dependent on the ratio of those circuit elements. No volts are missing. It's just physics!
Agreed. Electrician came over today saying that its fine as the earth wire can be omitted but i did not agree with him. Charged me 40 for a callout for nothing
Can i check continuity of earth from a nearby socket outlet earth by plugging a extension lead in and poking the earth prongs of it. Its suppose to beep right as the cpc are made common in the bus bar.
 
Agreed. Electrician came over today saying that its fine as the earth wire can be omitted but i did not agree with him. Charged me 40 for a callout for nothing
Can i check continuity of earth from a nearby socket outlet earth by plugging a extension lead in and poking the earth prongs of it. Its suppose to beep right as the cpc are made common in the bus bar.
I suspect the Electrician is looking at the ceiling rose, seeing twin cable to the light fitting, and saying 'nothing wrong here', but I agree with you there should be cpc continuity to the rose, ready for when someone connects a fitting that requires it.

If you check continuity as you suggest (preferably power off!), based on the evidence, I'd be willing to bet you'll see a high resistance, so the next logical step would be to find the break! Given the induced voltage, it may be some way back to where the power comes from!?
 
If there were continuity you could test from any earthed point to any other earthed point and read the resistance because all CPCs should be connected together as you say. However, as we suspect there is no continuity, and some induced voltage exists, your continuity tester might object to having significant AC voltage poked into it on a resistance test. So, if you want to do that, switch the whole installation off at the main switch first to ensure a valid reading.
 
When was this house built or rewired? Earth wires in lighting circuits became compulsory from 1966, but for at least a decade afterwards there were plenty of electricians who saw nothing wrong with adding or altering pre 1966 lighting circuits with T&E, but leaving the cpcs unconnected. Add in later electricians/DIYers doing more wiring and assuming the cpcs are actually connected to earth without testing, and it used to be nothing unusual to find lighting cpcs with induced or leaked potentials on them.
Hopefully, most have been dealt with by now, but there's bound to be some still out there.
 
Agreed. Electrician came over today saying that its fine as the earth wire can be omitted but i did not agree with him. Charged me 40 for a callout for nothing
Can i check continuity of earth from a nearby socket outlet earth by plugging a extension lead in and poking the earth prongs of it. Its suppose to beep right as the cpc are made common in the bus bar.
I'd have expected a call-out on a Sunday to cost at least triple that just for attendance (and realistically more with you being close to London), but nonetheless it seems like a poor resolution.
 
Agreed. Electrician came over today saying that its fine as the earth wire can be omitted but i did not agree with him. Charged me 40 for a callout for nothing
Can i check continuity of earth from a nearby socket outlet earth by plugging a extension lead in and poking the earth prongs of it. Its suppose to beep right as the cpc are made common in the bus bar.
40 quid for a callout on a Sunday?? Wouldn't get off my hole for that on a weekday!
 
I'd have expected a call-out on a Sunday to cost at least triple that just for attendance (and realistically more with you being close to London), but nonetheless it seems like a poor resolution.
True i hate the switches that I have got because the feed goes directly to the switch instead of going to the pendant itself. I have seen most newer builds not being like this!
 
True i hate the switches that I have got because the feed goes directly to the switch instead of going to the pendant itself. I have seen most newer builds not being like this!

Feeding to the switch is better than feeding to the pendant. For one thing it allows smart switches that need a neutral, and it also avoids having to fit masses of wire into a light fitting whilst holding it above your head.
 
DPG has given you some good reasons to do it this way.

Why do you hate it?
I think its because most people adhere to the 2 plate method switching which they teach in colleges etc. Having permanent lives at the switch has more chances of borrowed neutrals + it gets hard to add or rewire as the wires are commonly behind solid walls unlike having it wires in the pendant more likely has drywall.
 
I think its because most people adhere to the 2 plate method switching which they teach in colleges etc. Having permanent lives at the switch has more chances of borrowed neutrals + it gets hard to add or rewire as the wires are commonly behind solid walls unlike having it wires in the pendant more likely has drywall.
I agree, both methods have their advantages and disadvantages. I was just wondering why the OP "hated" one method over another. We all may have our preferred method.

I just thought it sounded a bit dramatic to state the word hate.
 
Yeah it is quite dramatic hehe but when the lighting is on a ceiling rose which they use in UK, it has a lot of terminals for the normal halogen or led lights but when upgrading to "fashiony" lights those wires must be omitted, i see most electricians just connect the loops together with a wago connector.
 

Reply to Strange voltage on earth wire in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
738
Old two core cable in a lighting circuit with no cpc at any point All points had metal fixtures and fittings class1 At two points the live loop...
Replies
0
Views
650
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
581
Hello, disclaimer: this is DIY and I am rather ignorant about electrical works. I just moved into a new rental apartment and i wanted to connect...
Replies
11
Views
614
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
702

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock