Hi I wonder if I could get a few opinions, randomly half of my house shuts off or flickers, this included the stove, lights, fans, clocks etc, then a minute or two later it comes back on, but no breakers ever trip. I had an electrician out and he suggested a loose neutral but never actually fixed anything. It is very random, sometimes doesn't happen for months then starts back up again. Any thoughts? Its not something I will attempt to fix but I'd like to have some thoughts before speaking to an electrician as the last guy seemed to think it was specific to an outlet or switch but couldn't explain how that would shut the stove off. Hydro was out and confirmed power to the meter was as expected but the randomness of the problem wasn't occurring while he was present.
 
Last edited:
As I wrote above then, but probably for a different reason.
Anything from, and including, the main switch backwards to where your supply connects to the supply to other properties, assuming you are the only one affected. Have you checked with neighbours?
 
What was that 'electrician' thinking?

One side of the panel fed by one hot leg / phase is OK.
One side of the panel fed by the other hot leg / phase is intermittent.
No breakers trip.

With 99.9% certainly the problem is upstream of the panel busbar and is a bad connection in the phase that is intermittent. Could be one of your components e.g. main breaker, or could be one of Hydro's e.g. meter socket. But it's not likely to be the neutral and it certainly isn't anything downstream of the busbar e.g. one of the ordinary breakers. The bad connection might already be overheated, discoloured, burnt etc. and might respond to wiggling.

Unless something very spooky is going on, this shouldn't have anyone stumped for long.
 
What was that 'electrician' thinking?

One side of the panel fed by one hot leg / phase is OK.
One side of the panel fed by the other hot leg / phase is intermittent.
No breakers trip.

With 99.9% certainly the problem is upstream of the panel busbar and is a bad connection in the phase that is intermittent. Could be one of your components e.g. main breaker, or could be one of Hydro's e.g. meter socket. But it's not likely to be the neutral and it certainly isn't anything downstream of the busbar e.g. one of the ordinary breakers. The bad connection might already be overheated, discoloured, burnt etc. and might respond to wiggling.

Unless something very spooky is going on, this shouldn't have anyone stumped for long.
Wow, that’s the answer hoping for, a confident one! Now at least I can have this conversation with the electrician, thanks a bunch Lucien!
 
Hi I wonder if I could get a few opinions, randomly half of my house shuts off or flickers, this included the stove, lights, fans, clocks etc, then a minute or two later it comes back on, but no breakers ever trip. I had an electrician out and he suggested a loose neutral but never actually fixed anything. It is very random, sometimes doesn't happen for months then starts back up again. Any thoughts? Its not something I will attempt to fix but I'd like to have some thoughts before speaking to an electrician as the last guy seemed to think it was specific to an outlet or switch but couldn't explain how that would shut the stove off. Hydro was out and confirmed power to the meter was as expected but the randomness of the problem wasn't occurring while he was present.
You are definitely loosing 1 leg of your hots coming in. If it was the neutral loose then everything would be acting up. It could actually be on the power company’s side, it could also be in the meter base, and it could also be a defective main breaker. Hire you another electrician and let him read this post. Good luck and let us know how it turns out.
 
You are definitely loosing 1 leg of your hots coming in. If it was the neutral loose then everything would be acting up. It could actually be on the power company’s side, it could also be in the meter base, and it could also be a defective main breaker. Hire you another electrician and let him read this post. Good luck and let us know how it turns out.
awesome thanks!
 
awesome thanks!
Dear Joe, has the issue been repaired? As, a technician, I experienced a fault, similar to this, in a farmhouse,
once in Essex, putting aside some very technical, reasons, consider keeping it to any simple causes, as well.
You have an intermittent fault, causing flickering, and "brown outs", i.e. not completely off, or trip of breaker.
Is this happening, in wet weather? In the farmhouse, rainwater, on a broken light fixture, did the short circuit.
It can be a general property maintenance issue, suggest checking, for any rainwater ingress, or a pipe drips.
Could also, be caused by a bathroom remodel, where fitter has not waterproofed, or capped old wiring right.
 

Reply to Stumped my electrician in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
855
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
653
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock