I can think of a couple of reasons what this may have taken place.
1/ Inexperience. The installer may have been told that he should install an additional 16mm CPC and did not know what to do with the incorporated 6mm CPC so just cut it off.
2/ Due to damage or a fault with its continuity found on a previous PIR/EICR
It is good practise to connect any unused or faulty conductors to earth, the reasons for this is that in the event of cable damage it is possible for this conductor to become live, (something like a nail strike for example) and cause the protective device not to operate. This could then cause a dangerous situation in that a voltage will be present where it would not normally be expected. By connecting unused or faulty conductors to earth this will also prevent transient or phantom voltages being present.
If the conductor is damaged or does not have continuity through its whole length and only one end is connected to earth this can cause the above issues on the united earthed section.
My recommendation would be to extend the cut CPC and connect both ends and connect to a earth connection following a continuity check to confirm the reason.
I would then make a comment on the observation section of any documentation you complete.