So, here's a thing. Not conventional for a domestic, and not cheap, but an adjustable RCD could in theory be set for bang-on 300mS @ 30mA / 40mS @ 150mA and be compliant, basically relying on the downstream devices being inherently faster (which we all know they typically are, by a significant margin).
The upstream RCD is probably seeing a lot more leakage than individual downstream RCBOs, because it's protecting the whole installation. It's likely to be closer to it's tripping threshold, so a small amount of leakage on a downstream circuit might push it over the edge, while failing to trip the downstream RCBO.
So the above might work, for some faults, might not.
 
The upstream RCD is probably seeing a lot more leakage than individual downstream RCBOs, because it's protecting the whole installation. It's likely to be closer to it's tripping threshold, so a small amount of leakage on a downstream circuit might push it over the edge, while failing to trip the downstream RCBO.
So the above might work, for some faults, might not.
Indeed, I would clamp the sub-main to begin with to get an idea of the margin for whatever approach is needed.

But if its is close to 15mA already I don't see any real solution without fixing the initial cable run's need for 30mA additional protection. By time you look at an adjustable solution, etc, the cost is getting seriously large and it might still be a bit flaky!
 
Indeed, I would clamp the sub-main to begin with to get an idea of the margin for whatever approach is needed.

But if its is close to 15mA already I don't see any real solution without fixing the initial cable run's need for 30mA additional protection. By time you look at an adjustable solution, etc, the cost is getting seriously large and it might still be a bit flaky!
You're of course absolutely correct and we've had this entire thread without me being on site again yet, however my suspicion is that there's probably no accumulative leakage to speak of at all, what we're dealing with is purely fault current. Downstream of all of this is basically just lighting and typical resistive/inductive stuff in a workshop or two.

As for costs.... the last one I did a couple of years back was around the same £7-800 mark, was a fancy all-in-one Schneider ELCB jobby.
 
So, here's a thing. Not conventional for a domestic, and not cheap, but an adjustable RCD could in theory be set for bang-on 300mS @ 30mA / 40mS @ 150mA and be compliant, basically relying on the downstream devices being inherently faster (which we all know they typically are, by a significant margin).
I wonder if that is what Scneider's "A-SI" really is? 30mA with a very short delay but still meeting times?

At £300 a bit much to buy one just to play with...
 
You're of course absolutely correct and we've had this entire thread without me being on site again yet, however my suspicion is that there's probably no accumulative leakage to speak of at all, what we're dealing with is purely fault current. Downstream of all of this is basically just lighting and typical resistive/inductive stuff in a workshop or two.

As for costs.... the last one I did a couple of years back was around the same £7-800 mark, was a fancy all-in-one Schneider ELCB jobby.
Yes, not cheap any how.

I suppose the irony is if this had been found with a 100mA delay RCD and so no "additional protection" it would only get a C3 inspection code!

Assuming no muppet ran the cable through the bathroom of course...
 
The chance of someone putting a nail or something in the cable just at the right spot to receive a shock, and a 100ma S rcd not tripping is highly unlikely, i would say they have more of a chance of being injured with the sudden loss of power.

The chance of a customer paying £1000s to sort out a random tripping problem is even more unlikely. :)
 

Reply to Suggestions for better RCD discrimination in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
772
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock